Just your thoughts on this one,had the plasterers moaning about live sockets.
Added a couple of sockets to an existing ring main,to keep the power on in the house I’ve connected & taped the cables & neatly coiled into the flush box.
The customer knows the reasoning behind this,& will talk to the plasterers,& advise them to switch the marked Mcb off.
The remarks from the plasterers were not too good,& you can imagine the stick & bad names floating around, pardon the pun there.
They done their bit,& no incidents of electric shock,but just bad mouthing.
Would you have done the same, or maybe I’m at fault.
 
When I've had to leave live cables in a flush mounting box, which will be plastered, I've fitted a metal cover plate that is cut slightly smaller than the box, so it recesses in as far as the lugs. So there is no access to the cables inside. The cover plate cut from thin sheet metal with tin-snips, and I retrieve them afterwards to reuse.
 
I always used to simply put connector block on the cables and coil up in the box , did it this way for years & years

then one day I had a plasterer have real moan saying on a different job he got a shock off a back box while plastering

so from that day I always put a blank plate on the box which had any live cables in
 
:eek:Always leave them live that way the muckspreaders pay a little more attention what they're doing with their towels.:eek:
[automerge]1596309465[/automerge]
:eek:Always leave them live that way the muckspreaders pay a little more attention what they're doing with their towels.:eek:
Trowels, flaming auto correct
 
I always used to simply put connector block on the cables and coil up in the box , did it this way for years & years

then one day I had a plasterer have real moan saying on a different job he got a shock off a back box while plastering

so from that day I always put a blank plate on the box which had any live cables in
i've always done that if the cables have needed to be energised to complete a circuit. some years ago, i fitted the sockets on 4 outlets with yoozy boxes. thinking easy for the plasterer and also safe. i turn up next day. all 4 socket faceplates covered in muck and all 4 yoozy boxes broken.
 
You need to ensure that there is no way that the plasterer, or anyone else can be put at risk.

There is no perfect solution to this problem, other than leaving the circuit isolated which is sometimes not possible in the real world.
 
As far as health and safety is concerned, all you can do is isolate.

your leaving live cables with only basic insulation. Even behind a bit of cardboard or plastic... plasterer is throwing water all over the place and using a sharp metal object. If they’ve had an incident before, I’m not surprised they complain.
 
I dont think i can ever recall expecting a plasterer to work on a live socket regardless of any tape, bags or anything else. I would expect to isolate, prior, keeping disruption to a minimum by supplying temp power from other sources.
The house i am currently working on , I isolated the section of the ring to keep some power on for his mixer etc. There are nearly always a work around, more puzzled about how its common to leave the power on. What possible scenario would that be ? The only socket in the place ? ...lol
 
Just isolate the ring and provide them with a builders supply on a trailing socket. Simples!!
 
When I've had to leave live cables in a flush mounting box, which will be plastered, I've fitted a metal cover plate that is cut slightly smaller than the box, so it recesses in as far as the lugs. So there is no access to the cables inside. The cover plate cut from thin sheet metal with tin-snips, and I retrieve them afterwards to reuse.
Circuit feeding sockets should be isolated and locked off until plasterers are finished.
 
Circuit feeding sockets should be isolated and locked off until plasterers are finished.
In the example I gave, they were not sockets, but light switches, which would be very inconvenient in an occupied property where the other lights on the circuit need to remain in use. It would be a week or two before the plastering is done.

I would also add that I include a large label in the outside of the metal cover that the circuit inside is live.
 