I am using the relays of a control panel to switch on a single phase contactor. This contactor then turns on a motor. The relays are 24V dc rated and inside this control panel there is electronic circuitry. I am worried that the back emf created by the contactor coil might damage the relays or even worse, damage the electronics inside the control panel. Would it be better to use a solid state single phase contactor rather than the conventional contactor to prevent this?
 
i wouldnt bother, i dont know your exact apllication but i dont think the back emf produced by a collapsing 24v coil will cause your electronics much bother. if it helps you sleep better connect a diode in parallel and in opposition with the coil
 
To prevent arcing accross contacts and to dissipate the back EMF safely a free wheeling diode is connected in parallel (anode on minus) to the coil. This way it doesn't conduct normally. When the coil is switched off, the voltage across the coil reverses to maintain the current's direction. Then the diode carries the current until the energy is consumed by the coil's inner resistance.

This can be used for DC only. For AC use resistor/capacitor (RC) network
 
Hi,

Thanks for that. I'm pretty sure these surge suppressors can be easily purchased so I will do as you say!!

Thanks for that.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Solid state contactor???
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
gerard,
Last reply from
gerard,
Replies
4
Views
1,828

Advert

Back
Top