Hi guy's, Newly qaulified electrician here just after some help/advice.
I apologise this may be a bit long winded.

On my first job which is a small extension on a fairly old property, putting in new circuits for sockets, lights etc. The customer has also asked me to alter a lighting circuit in the downstairs area of the house, however upon investigation i discovered the circuit has no cpc. The circuit includes her lounge, kitchen/utilty and wc. She has not long had some work done in the kitchen which included 15 new downlights, new sockets and under cpd lights. They also installed a new consumer unit. They have joined into the lighting circuit which has no earth and obviously i couldn't get any continuity readings. I asked her if they had issued her a certificate, which they did. I took a quick look discovered they had not put any readings for R1 R2's on said lighting circuit. The columns were just left blank. The section for departures from BS7671 was left blank but in the comments he has written "1 lighting circuit needs re-wiring". The certificate is written out in pen, and a lot of boxes are left blank without N/A. I asked the lady if he had mentioned about the lack of a cpc in the lights but she said he did not.
The certificate is NICEIC and along with the test results it also has a certificate of compliance.
This may sound like a daft question but would the NICEIC allow a certificate to be completed like this or has he skipped notifying the work and issued a dud cert?
Any help would be great. Im with Napit by the way.

Cheers
Chris
 
Hi guy's, Newly qaulified electrician here just after some help/advice.
I apologise this may be a bit long winded.

On my first job which is a small extension on a fairly old property, putting in new circuits for sockets, lights etc. The customer has also asked me to alter a lighting circuit in the downstairs area of the house, however upon investigation i discovered the circuit has no cpc. The circuit includes her lounge, kitchen/utilty and wc. She has not long had some work done in the kitchen which included 15 new downlights, new sockets and under cpd lights. They also installed a new consumer unit. They have joined into the lighting circuit which has no earth and obviously i couldn't get any continuity readings. I asked her if they had issued her a certificate, which they did. I took a quick look discovered they had not put any readings for R1 R2's on said lighting circuit. The columns were just left blank. The section for departures from BS7671 was left blank but in the comments he has written "1 lighting circuit needs re-wiring". The certificate is written out in pen, and a lot of boxes are left blank without N/A. I asked the lady if he had mentioned about the lack of a cpc in the lights but she said he did not.
The certificate is NICEIC and along with the test results it also has a certificate of compliance.
This may sound like a daft question but would the NICEIC allow a certificate to be completed like this or has he skipped notifying the work and issued a dud cert?
Any help would be great. Im with Napit by the way.

Cheers
Chris

Was the installers number on the cert and has the customer looked the individual up?
 
Was the installers number on the cert and has the customer looked the individual up?

Yes their was an installers number on the cert, Not sure if the customer has looked them up. Will ask how she got hold of him.
 
A lighting circuit without a cpc need not necessarily be rewired as long as any luminaires and accessories are class 2. If a cu change is carried out the circuit should be checked for class 1 fittings/switches etc and an assessment made of their safety.This can be checked by carrying out an insulation test between the unearthed metalwork (conductive parts) and the L/N of the circuit joined together,a high reading would indicate that class1 fittings are safe to leave,however a notice should be provided at the CU indicating there are lighting circuits lacking a cpc...(ready made notices are available)...and the cert filled in accordingly. No alterations or additions to a circuit without a cpc are permitted with the exception of connecting such a circuit to a new CU as above if the client wont consider rewiring.
Have a look on the Electrical Safety Council website and there is a best practice guide which NIC contractors should be adhereing to

Best practice guides : Electrical Safety Council
 
A lighting circuit without a cpc need not necessarily be rewired as long as any luminaires and accessories are class 2. If a cu change is carried out the circuit should be checked for class 1 fittings/switches etc and an assessment made of their safety.This can be checked by carrying out an insulation test between the unearthed metalwork (conductive parts) and the L/N of the circuit joined together,a high reading would indicate that class1 fittings are safe to leave,however a notice should be provided at the CU indicating there are lighting circuits lacking a cpc...(ready made notices are available)...and the cert filled in accordingly. No alterations or additions to a circuit without a cpc are permitted with the exception of connecting such a circuit to a new CU as above if the client wont consider rewiring.
Have a look on the Electrical Safety Council website and there is a best practice guide which NIC contractors should be adhereing to

Best practice guides : Electrical Safety Council

Many thanks chap, help is appreciated. They are class 1 fittings on the circuit
 