Hello,
I have a Leviton 51120-1 SPD connected to a residential (120/240V) 200A breaker/service main panel – The 51120 is fed from (2qty) – 20A breakers in the service panel – All wires connected to the 51120 (L1&L2 hot, neut,& ground) are 12 AWG stranded conductors – The install instructions indicate the terminal block accepts 4 to 12 AWG solid or stranded conductors - Should these conductor size be increased to 10 AWG or to solid AWG conductors or to something else ?
Thank you.
I have a Leviton 51120-1 SPD connected to a residential (120/240V) 200A breaker/service main panel – The 51120 is fed from (2qty) – 20A breakers in the service panel – All wires connected to the 51120 (L1&L2 hot, neut,& ground) are 12 AWG stranded conductors – The install instructions indicate the terminal block accepts 4 to 12 AWG solid or stranded conductors - Should these conductor size be increased to 10 AWG or to solid AWG conductors or to something else ?