Discuss spd in meter box? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Client needs an SPD fitting but no room in c/u or adjacent. Best bet looks like a parallel connection into the tail blocks in the meter cabinet with an adjacent 'standalone unit' ie with overcurrent protection. Anybody done this? Any reason I shouldn't? Is it ok to use board PEN connection block for earth?
 
Wylex do a tail isolator with type 2 SPD that's rated at 100A so no need to fuse down. This is what I would use just make sure you get your supply and load around the right way round.
Screenshot_20240402_185943_Samsung Internet.jpg
 

Same idea but 1/4 the price...! Have fitted both and not a huge difference in quality tbh , Wylex obvs the benchmark though but I'll be mostly fitting the WCED ..
 