In truth, I am a bit sceptical about SPD's, especially if you are hit multiple times, which has happened on more than one occasion to our place, even though we have SPD's in place, I still unplug everything when a storm hits and when we leave the place for any period of time.
 
One SPD covering the whole installation won't protect sensitive equipment.

Type 1 for atmospheric i.e lightning
Type 2 for supply surges
Type 3 for sensitive equipment

Types 1 & 2 to protect the fixed installation, Type 3 to protect equipment.

An SPD won't stop a surge but reduces it's impact to more manageable levels. So Type 1/2 at source then Type 3 at socket-outlets.
 
All true, that's why I unplug everything when a storm is brewing, the coming of a storm is usually indicated by the TV Satellite picture pixelating, time to turn it off and unplug :cool: :eek: open a bottle, go to the window and watch the show, one hit a few years ago and was close enough that it unlocked my car and turned on the dashboard and lights.
 
All true, that's why I unplug everything when a storm is brewing, the coming of a storm is usually indicated by the TV Satellite picture pixelating, time to turn it off and unplug :cool: :eek: open a bottle, go to the window and watch the show, one hit a few years ago and was close enough that it unlocked my car and turned on the dashboard and lights.

TV pixelating is down to the heavy rain droplets as that has a big effect on signal strength (for satellite TV, terrestrial broadcast in UHF is hard to impact that way) and thus picture quality.

Depending on where you are that means either very wet, or lighting AND very wet...
[automerge]1584981093[/automerge]
The real issue is inductance, as for a short lighting pulse that will be a far higher impedance then the resistance we know and love/hate for AC power!

The IET says max distance for SPD wiring is 1m, but recommands less than 0.5m. So probably if the length from the Henley block (or whatever) to the SPD inside the CU with them fitted including internal CU wire lengths is below 0.5m you are fine.

If you are in an area of high risk, say you have overhead feeder cables, etc, then you ought to have a Type 1 SPD first then anyway as they can cope with a lot more energy than the Type 2 used for your typical board.

As already mentioned, most have a maximum protection fuse/breaker limit. For many SPD it is around the 100A-160A region so the DNO fuse is usually sufficient. Some it is less and you will see a dedicated 32A (or similar) MCB just for the SPD.

Some have the option for "V wiring" (Kelvin connection) where there are two terminals for each phase and neutral connection so you route the power "through" the SPD to minimise series wiring inductance. For that there may be an additional current limit based on the size of the internal conductor path as it may not be up for more than 80A/100A or whatever, even if the SPD can cope with a 160A supply fuse for absolute worst-case fault conditions.
 
Last edited:
Yes commonly called Rain Fade, the size of the main board being a four zone vertical unit it's very difficult to get the SPD wiring below 500mm, the dedicated MCB for the SPD is 20A, underground feeder cables, have we not had the conversation before?
 
The manufacturers should probably not be relying on the DNO fuse for short circuit protection as it would interrupt the continuous supply of the power to the installation if there was a short circuit fault.
I’m my mind you should install SPD’s with either built in ocpd or install an upfront ocpd.
I mean ,do the dno allow their fuse to be used in this manor?
 
Just in case, I was not complaining, always interested on others input.
[automerge]1584982294[/automerge]
Don't have a DNO fuse, it's a 500mA type S MCB, its main use is to cut the power if the consumer tries to draw more power than the tariff they are paying for.
 
It was a comment really about manufacturers who do not provide an ocpd in the consumer unit , like Hager, for their SPD’s.
I don’t think the dno fuse should be used for the purpose of providing protection to an SPD
 
Sorry Ian jumped the gun a bit, but I take your point, the SPD should have a dedicated OCPD, I guess Hager look at the fact they don't supply all the MCB's required for the installation, should they for the SPD? don't know the answer really.
 
I guess there is a point that for a domestic CU they typically won't be fused more than 100A (at least in UK) and none provide dedicated protection for the main switch (that is normally 100A rated) I guess for that reason.

The SPD (or at least any good ones) have internal thermal disconnect on overheating which is typically what throws the "end of life" indicator when that joint melts and opens the connection.

I don't think metal oxide varistor (MOV) types have a fail-short mode to worry about, but they can blow open on really big surges (as everything will do in the end). The gas discharge tube (GDT) ones typically see in Type 1 for higher energy handling might have a fail-short worry, or at least an arc sustain on the AC power afterwards. Some GDT-based SPD have a MOV in series, maybe to help with that fault mode, and/or make it easier to quench the arc post-flashover. The suppliers don't tell you much.

An advantage of a MCB for the SPD is it is simple to isolate for testing, more so if you lack the plug-in units, and it just feels better to have a known limit on fault current. Down side is the increase in series inductance and the degradation in protection, oh well, nothing is ever for free...
 