All true, that's why I unplug everything when a storm is brewing, the coming of a storm is usually indicated by the TV Satellite picture pixelating, time to turn it off and unplug

open a bottle, go to the window and watch the show, one hit a few years ago and was close enough that it unlocked my car and turned on the dashboard and lights.
TV pixelating is down to the heavy rain droplets as that has a big effect on signal strength (for satellite TV, terrestrial broadcast in UHF is hard to impact that way) and thus picture quality.
Depending on where you are that means either very wet, or lighting AND very wet...
[automerge]1584981093[/automerge]
The real issue is inductance, as for a short lighting pulse that will be a far higher impedance then the resistance we know and love/hate for AC power!
The IET says max distance for SPD wiring is 1m, but recommands less than 0.5m. So probably if the length from the Henley block (or whatever) to the SPD inside the CU with them fitted
including internal CU wire lengths is below 0.5m you are fine.
If you are in an area of high risk, say you have overhead feeder cables, etc, then you ought to have a Type 1 SPD first then anyway as they can cope with a
lot more energy than the Type 2 used for your typical board.
As already mentioned, most have a maximum protection fuse/breaker limit. For many SPD it is around the 100A-160A region so the DNO fuse is usually sufficient. Some it is less and you will see a dedicated 32A (or similar) MCB just for the SPD.
Some have the option for "V wiring" (Kelvin connection) where there are two terminals for each phase and neutral connection so you route the power "through" the SPD to minimise series wiring inductance. For that there may be an additional current limit based on the size of the internal conductor path as it may not be up for more than 80A/100A or whatever, even if the SPD can cope with a 160A supply fuse for absolute worst-case fault conditions.