You are actually not looking at the length of the cable, the 50 metres squared relates to the floor area served by the circuit you are installing. So wherever your radial goes, check out the size of the room or rooms served. Calculate the combined area, historically it has been limited to 50 metres squared!
Then you have to check out the other design criteria, likely Zs, operating times for CPD, volt-drop, etc.
Check page 426 in your regs book for radial circuit arrangements.
 
Back in sensible mode.

Basically, the area is irrelevant.
As you say above, as long as the cable meets the design criteria, it can be as long as you want, covering any area. (?)
 
How man! Divvent yee caal wor lass Sharon! Hor nyem is Sandra an if ye reckon Aa divvent knaa worram taalkin aboot, read the beuk
Sharon an Tracey worron Bords Of A Feather man

Aye ... 'n' them were Cockney bords not Geordie bords an'all.
 
Actually the area is very relevant to the original question, and is also mentioned in the Regs, as the overiding indicator of whether a radial protected by a 20A cpd, or a radial with 30/32A cpd, or a ring final circuit should be installed. Once the 'type' of circuit has been decided, then all the other design criteria can be determined.

I think maybe the original text of the question got lost in amongst the banter and beer talk? Still,it was a Saturday night and boys will be boys.
 
Actually the area is very relevant to the original question, and is also mentioned in the Regs, as the overiding indicator of whether a radial protected by a 20A cpd, or a radial with 30/32A cpd, or a ring final circuit should be installed. Once the 'type' of circuit has been decided, then all the other design criteria can be determined.

I think maybe the original text of the question got lost in amongst the banter and beer talk? Still,it was a Saturday night and boys will be boys.

........... and we all want to join the 3000 club. ;)
 
depending on loadand installation method page 61 osg says 31 m but this errrs on the side of safety for humty dumptys so do calcs out and maybe find it ok for lot more, but yes depends on load expected...