Hmmm, MCBs are upside down, copper showing at the terminations, confusing conductor identification.Looking at the other thread, it's an HMO with 12 rooms that might be separately let. If the communal GCH packs in. 12 x 2kW fanheaters will go on. There are also some electric hobs.
Returning to the subject of terminating 16 & 25mm² in DB's, we sometimes have to do this where the cable has been selected for VD or running through very high ambient temp. A terminal pin is OK, it won't automatically reduce the CCC, but then typically you won't hit the CCC with the kind of outgoing way you will have in a regular 60898 DB. Beware the effect of poor quality terminals though, sometimes they don't hold well on a solid lump of copper. Tthe same is true of solid MI cores which can be a problem to terminate in marginal single-screw terminals.
An alternative is to use an inline uninsulated butt crimp sized for the SWA core, with a tail of smaller cable with the correct number of strands carefully doubled over inwards, so that all strands contact the crimp. A suitable length tail will allow flexibility to minimise stress on the terminal.
I have been known, when pressed, to put three strands in one hole and four in the next, but I don't recommend it. I would be more likely to do this on an outsize EC, where it also gives the advantage of redundancy.
FWIW here's a pic of a 60898 board with 3x 3-phase 50A outgoing circuits in 16mm², admittedly conduit cable. I didn't wire the straggly stuff in the background, only the 16mm.
View attachment 39943
Codes C2, C2 & C3.