Discuss Stat wiring, I've adjusted in the Central Heating Systems area at ElectriciansForums.net
Hi all,
Have I wired this right, adding underfloor heating to a S plan opened the stat to check connections and it was just wired to the right hand side stat only I've re done it to the picture so the brown goes Rob the limiter first, that right?
Cheers grand
They are in series, so it don't matter.
PS, the left hand limiter needs earthing too!
PPS, the blue conductor needs to have a brown sleeve on it.
PPPS Don't forget to ensure the flex outer sheath is inside the stat
Just to check:
we are looking at the temp controls for an unvented tank (Megaflo, etc)?
And that bit of flex is part of the DHW control circuit?
Yes both stats must be in series, only having the right hand stat connected was dangerous, you've done the correct thing there.
Those units are normally double insulated so connecting the earth is not necessary, but if you are going to connect it then connect it to both metal bits, not just one.
Are you sure it's an S plan system as there appears to be a black wire connected to the DHW off terminal of the stat, this would suggest a Y plan system.
If it is a Y plan system then you should confirm that the necessary additional 2 port valve for the overheat protection has been installed. If the installer didn't connect the overheat stat they may have ignored other essential safety devices.
Reply to Stat wiring, I've adjusted in the Central Heating Systems area at ElectriciansForums.net
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
At our church, one of the things I've done is sort out the heating wiring (as best I can for now). The schematic is as shown below. The theory...
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Hi all, I did train as an electrician but never worked as one so my experience is limited and ive not done anything for a while now. I have an...