Discuss Strange loop values in the UK Electrical Forum area at ElectriciansForums.net
J
Jimmyb
Im I missing something ?
been checking 2 x ring finals yesterday and found the following results :-
R1 Rn R2 R1+R2
0.36 0.36 0.45 0.18 for length of est circuit r1&rn values seem about right
0.47 0.47 1.38 0.35 cant check length with this but most be loose cpc somewhere
I thought well ill check for loose connection on both and found nothing, well I checked all accessible one/what I could find
anyone else got thoughts on this please there is only loose damaged connection
You're 95% correct. I always have an issue with the term loose connection. It's poor connection to me.
It doesn't necessarily mean theres a 'loose connection' anywhere - as you've pointed out you can't find it. You could literally open every single socket and find everything tight.
It could mean that the insulation of the cable is nicked instead of the copper at one of the connections somewhere on the ring.
It could also mean theres a socket that you haven't found that has a 'loose connection' or even a damaged cable end thats just about hanging on in there at the terminal.
But yes you're correct, it's a 'loose connection' as you put it somewhere.
Sounds like more than a loose connection looking at that R1+R2 figure on the first RFC. Daz
Is this a new installation or old. Have you checked R1 + R2 at terminal connections at back of sockets as opposed to socket outlet fronts, as results can vary considerably due to tarnishing and wear ?.
The R2 value can't be 'better' if it's incorrect though can it. Daz
I would suggest that ring 2 may have a poor connection in an inaccessible joint box, or the cable type being older may have a smaller cpc than you expect.
Have not read all of the post but firstly id be looking for any noticable alterations and starting there. It will more than likely be a poor connection in a junction box under floor boards or connections made of behind a kitchen unit for example. Or try following a logical route using "long lead" method and notin any considerable rises in test values to pin point the location of the fault
Reply to Strange loop values in the UK Electrical Forum area at ElectriciansForums.net
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
