Fault Rectified !!! This evening I disconnected each leg of the ring, plus the spurs from jb's. IR'd every individual leg, every single one clear. Reconnected one leg at db and 1st socket, carried out ramp test and got 26mA. connected the next socket, ramp tested and got 26mA. so on and so on until after connecting another leg the ramp tester would not trip, gave >51mA as a reading. left this leg out of the ring, reconnected everything else, ramp tested 26mA and plugged in the loads, happy days. Rewired faulty leg and bobs your uncle problem solved.
What I've learnt from this fault -
1. I need to buy a ramp tester as I would never have found the fault otherwise.
2. I hate faults !
3. Insulation resistance alone doesnt always identify a faulty cable (although this one is still baffling me why the leg IR'd clear yet it was causing the fault)
.
Thank you for all the help and advice on this one.
I had almost identicle IR readings to you a couple of weeks back.
I got .5Meg between leg 1 line and Leg 2 Earth with all sockets connected but fault vanished when you disconnect all points.
When i connected the earths back in the db and retested the fault was back.
Took a while to find but turned out to be a screw through the line that was touching a bonded water pipe so the fault only appeared when the earths were connected in the db. Spent a couple of hours with a wander lead to finally trace the offending cable. Luckily it was roughly center of the ring so i converted it to 2 16a radials as they didnt fancy me chasing their newly decorated walls.
Tim