I'm glad you found the fault! I was thinking, though, about having found it with the ramp test. I'm not knocking your work, just musing on what the actual fault was and how it might have been found by testing when dead rather than energised.
The ramp test is responding to the symptom, i.e. that the RCD misbehaves, rather than the fault itself, i.e. that the cable is damaged. If you'll allow me an analogy, it's like finding a water leak by changing pipes length by length until your water bill drops. But the leak itself should be visible, and so might the cable fault have been detectable with the insulation and continuity tests.
Did you at any point test from all conductors of the faulty RFC (disconnected at the CU) to the rest of the installation globally, including earth? Or from all cores of the isolated faulted leg to the rest of the RFC? If you did not have a definite clear reading of those, it is possible that there is still a fault between the disconnected faulty leg of the RFC and another cable, although it might no longer show up from the other circuit because the RFC side of the fault is disconnected.
Put another way, a cable that passed (within reason) a IR test between all its conductors, but which causes random RCD tripping and also causes an RCD test to fail, must be significantly faulted to something else. As yet I don't think there is any proof that the fault is only to earth (although that is the most likely) but there is some evidence that it is not to earth (your cross-legged IR results and the fact it causes the ramp test to fail without an N-E short).
Perhaps you had other results that proved it one way or another, would be interested to hear.