SimpleSimon

Hi guys

Trying to diagnose a street light, a Thorn Beta 5 with 35W SOX lamp. Replaced the lamp and the fuse, went to turn it on and it came on for a couple of seconds trying to light up than blew the fuse.
Does anyone know if this is the ignitor or Ballast doing this? Just want to get the right part before I go all the way up there. Also where would one find these parts :icon10:

Thanks

Simon
 
To be honest Simon I would be looking to move the control gear down to ground level. Saves a lot of pratting about in the future.
 
we tended to replace both as matter of course If ballast has gone then the ignitor is trying to ignite thus shortening its life if its the ignitor thats gone then it has possibly put strain on ballast with same effect As for mounting gear in base this can cause problems with lenmgth of cable to lampholder and chaffing in coloum the chances of needing to replace it often enough outweigh the possible advantage of base mounting gear Forby the space in base door isnt the greatest

BUT depending on client due to greeness of SOX stuff you could try n persuade them to go the Halide route or led route
 
Last edited by a moderator:
To be honest Simon I would be looking to move the control gear down to ground level. Saves a lot of pratting about in the future.

Wouldnt want to do that on this occasion Tony. On a local gypsy site and ive already returned twice with the lid hanging off :(

Sent from my GT-I9100 using Tapatalk
 
apart from the Lid and other stuff dampness caused by condensation can cause tracking on ignitors , ballast
 