Need to supply a sub main in a farm mechanical workshop need to work out cable size earthing isolation want to have about 40 amp supply about 5 meters run on catinary just wondered what would people do. Already have 8 way board with 30ma at end of circuit
 
can you not run SWA buried? much neater job. 6mm or 10mm XLPE SWA.
 
so 6mm XLPE SWA, well capable of 40A. decent catenary. can you go high enough to be above wagons on the weighbridge?
 
50A is borderline for 6mm. google AEI cables and use their cable finder wizard.it calcs VD as well could poss. get away with 6mm XLPE, allowing for diversity.10mm XLPE is rated 81A, be inclined to export earth from cut-out or you will have to RCD alll circuits to achieve disconnection times if TT.. 63A switch fuse at supply end (10mm) . CU and RCD/RCBOs workshop. bear in mind only sockets need RCD as long as other circuits are surface wired. (TN earting)
 
Last edited:
300 ma??? what reg. is that?
 
I would just string some 6mm twin+e enclosed in plastic conduit and tie it to the catenery wire
An swa cable would be better,but if it cant be buried,its weight on the catenary would outdo any advantages
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
sub main
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
dochisholm,
Last reply from
Des 56,
Replies
10
Views
1,860

Advert