Piratepete

I was going to feed a distant 3ph dis board from the distributor's meter via a local 40Amp 3ph switchfuse. The distributor's fuses are 100Amp BS1361 Type II. It's PME.

I've got limited space for the switchfuse. Distance to the Dis board (which will have a 30mA RCD mainswitch) is about 20 metres.

Am I allowed to use a triple pole MCB instead of the Switch fuse with BS88 fuses? Or is the kA rating of MCBs (6 or 10kA) too low for this use?

Thanks

Pete
 
if you are feeding 3øand N, i think you'll need a 4 pole .
 
i'm not sure on this, but DNO always ask for a 4 pole on PME.
 
yes its perfectly acceptable to connect a 3 phase submains to a mcb.
if its not i'm in deep crap cos i've done dozens like that lol. ;-)

as for short circuit rating , well that depends on your pfc , but newer 3 pole mcb's are often 10ka rating anyway so shouldnt be a prob.
 
It depends on whether the cable to the sub supply is mechanically protected or not as to whether it needs 'additional protection'

Hi
The question is about the principle of replacing the traditional switchfuse by an MCB. Cable is SWA.
Pete
 
Oh sorry, my brain read 'RCD' instead of 'MCB' for some odd reason!

The issues with using an MCB are the lower fusing factor... so a fault on a 32A ring might also take out the 40A MCB you're adding. So long as you have a low enough Zs I'd look at using a type C. And as mentioned the PFC rating...which can be settled by doing a quick test :)
 