Piratepete
I was going to feed a distant 3ph dis board from the distributor's meter via a local 40Amp 3ph switchfuse. The distributor's fuses are 100Amp BS1361 Type II. It's PME.
I've got limited space for the switchfuse. Distance to the Dis board (which will have a 30mA RCD mainswitch) is about 20 metres.
Am I allowed to use a triple pole MCB instead of the Switch fuse with BS88 fuses? Or is the kA rating of MCBs (6 or 10kA) too low for this use?
Thanks
Pete