Thanks for all the responses, guys. I'll see if I can apply a little diversity and feedback on cable sizes. Speaking to him further, they have already spoken to National Grid, who have advised running the submain rather than a new supply; they may well be serious.
 
My opinion is that the 3% allowed voltage drop for lighting is unnecessarily restrictive. For a project such as this, I would disregard it and work to 5%.
Good reply, my post wasn't supposed to be flippant. It's just that I have never seen (or heard from anyone on here) of an appliance or light not working due to VD (in a domestic situation). I also don't remember ever reading a thread where VD has even been a problem, and it's been quite a few years on here now.

'A little silly' was perhaps the wrong phrase. Perhaps 'unnecessary in some situations' would be better. LED lighting can work at far lower voltages for instance, so a 5% VD for lights is going to be fine. However, it's not to our bible!!
 
I've never taken that much notice of the 3% VD for lighting since LED became the norm.
Are you sure your calculated load is realistic? We can't really comment on that without knowing what the usage of the buildings is, but on the other hand, it's important that the cable isn't too small and things start tripping on a regular basis.
 
Technically the 3/5% public supply limits on voltage drop are in an Informative appendix, and therefore not actually a Regulation. Though the requirement is "deemed to be satisfied" if these limits are met.
 
Good reply, my post wasn't supposed to be flippant. It's just that I have never seen (or heard from anyone on here) of an appliance or light not working due to VD (in a domestic situation).
I also don't remember ever reading a thread where VD has even been a problem, and it's been quite a few years on here now.

I'm sure there have been threads discussing it in the past, I'm sure I've contributed to them under a previous username.
There have been discussions about lights dimming when electric showers are switched on, I know this is usually VD in the DNO network rather than the installation, but could equally happen on an undersized submain.


'A little silly' was perhaps the wrong phrase. Perhaps 'unnecessary in some situations' would be better. LED lighting can work at far lower voltages for instance, so a 5% VD for lights is going to be fine. However, it's not to our bible!!

A Larger voltage drop will be fine for that kind of load yes, but will it be ok for the cable?

Don't forget that the voltage drop is just a product of resistances in series, the resistance of the cable being put in series with the load. So, as with any circuit of resistors in series, the greater the voltage drop across the resistor, the more power (as heat) is dissipated by it.

Obviously with an LED lighting circuit you wouldn't see any appreciable temperature rise in the cable in even an extreme case, but the rules have to cover all possible cases.
 
As long as the current is less than the maximum current for a conductor of the size installed and for the method of installation used, which for sub mains of this length it will always will be, there is no danger of overheating the cable.
The longer the cable, the more total heat will be generated, but that doesn't increase the heat generated per unit length of cable.
 
I'm sure there have been threads discussing it in the past, I'm sure I've contributed to them under a previous username.
There have been discussions about lights dimming when electric showers are switched on, I know this is usually VD in the DNO network rather than the installation, but could equally happen on an undersized submain.




A Larger voltage drop will be fine for that kind of load yes, but will it be ok for the cable?

Don't forget that the voltage drop is just a product of resistances in series, the resistance of the cable being put in series with the load. So, as with any circuit of resistors in series, the greater the voltage drop across the resistor, the more power (as heat) is dissipated by it.

Obviously with an LED lighting circuit you wouldn't see any appreciable temperature rise in the cable in even an extreme case, but the rules have to cover all possible cases.