I've been asked to run 280m submain to a remote building to feed a distribution board, which will have a lighting circuit and three radials.

If I make it 25mm, I'm still getting a volt drop of 13.29. Do we have any wiggle room on Volt Drop? Given that we are actually on 240V and most stuff will run at 220V.
 
I've been asked to run 280m submain to a remote building to feed a distribution board, which will have a lighting circuit and three radials.

That is a long run!
If I make it 25mm, I'm still getting a volt drop of 13.29. Do we have any wiggle room on Volt Drop? Given that we are actually on 240V and most stuff will run at 220V.
No wriggle room otherwise the install doesn't comply with BS7671. If the supply is from a Private LV you get slightly less volt drop requirements.

Technically the voltage is 230V we harmonised with Europe.

Don't forget that the supply can vary 216V to 253V and be within limits.
I've had to make assumptions, for the radial I've gone with 3kW, 240W for the lights (6 * LED batten), 500W for the pump and gone with 2.5kW for the polly tunnel. I'm making that 27.13 Amps.
What is the building going to be used for? Can you apply diversity?

Unless you can get the design current down the minimum cable size would be a 70mm. Don't forget that is only the volt drop to the sub panel and not the overall volt drop.

Can you make it work with 2 or more cables?

I take it getting a separate supply installed is out of the question? It might be more cost effective.
 
That is a long run!

No wriggle room otherwise the install doesn't comply with BS7671. If the supply is from a Private LV you get slightly less volt drop requirements.

Technically the voltage is 230V we harmonised with Europe.

Don't forget that the supply can vary 216V to 253V and be within limits.

What is the building going to be used for? Can you apply diversity?

Unless you can get the design current down the minimum cable size would be a 70mm. Don't forget that is only the volt drop to the sub panel and not the overall volt drop.

Can you make it work with 2 or more cables?

I take it getting a separate supply installed is out of the question? It might be more cost effective.
Hi PS, thanks for your reply.

It is a long run.

He wasn't that specific, just said he wanted lighting, half a dozen sockets, a feed to a pump and then another to a polly tunnel. I've messaged them to be a bit more specific (and suggested getting a quote for a new supply to the building location).

I'm generally just a jobing sparks, could you please explain how 2 or more cables would help me?

Tony.
 
Hi PS, thanks for your reply.

It is a long run.

He wasn't that specific, just said he wanted lighting, half a dozen sockets, a feed to a pump and then another to a polly tunnel. I've messaged them to be a bit more specific (and suggested getting a quote for a new supply to the building location).

I'm generally just a jobing sparks, could you please explain how 2 or more cables would help me?

Tony.

Lighting has the most onerous VD requirement at 3% so you could run 2 supplies (Not ideal I know) and try to split the loads so you can achieve the VD requirements.

If you can't get a new supply put in you are going to have to reduce the design current some how. Client won't be able to run as much as they would like.
 