Rule of thumb is to allow 2% volt drop on a submain which results in 150.0mm².
If you use 3% you get 95.0mm².
Lighting has the most onerous VD requirement at 3% so you could run 2 supplies (Not ideal I know) and try to split the loads so you can achieve the VD requirements.
Does anyone else think the calculated cable size needed to counteract VD is sometimes a little silly?
My opinion is that the 3% allowed voltage drop for lighting is unnecessarily restrictive. For a project such as this, I would disregard it and work to 5%.No, why do you think it would be silly?
Good reply, my post wasn't supposed to be flippant. It's just that I have never seen (or heard from anyone on here) of an appliance or light not working due to VD (in a domestic situation). I also don't remember ever reading a thread where VD has even been a problem, and it's been quite a few years on here now.My opinion is that the 3% allowed voltage drop for lighting is unnecessarily restrictive. For a project such as this, I would disregard it and work to 5%.
Good reply, my post wasn't supposed to be flippant. It's just that I have never seen (or heard from anyone on here) of an appliance or light not working due to VD (in a domestic situation).
I also don't remember ever reading a thread where VD has even been a problem, and it's been quite a few years on here now.
'A little silly' was perhaps the wrong phrase. Perhaps 'unnecessary in some situations' would be better. LED lighting can work at far lower voltages for instance, so a 5% VD for lights is going to be fine. However, it's not to our bible!!
All I'm really interested in is "what was your previous username?"I'm sure there have been threads discussing it in the past, I'm sure I've contributed to them under a previous username.
There have been discussions about lights dimming when electric showers are switched on, I know this is usually VD in the DNO network rather than the installation, but could equally happen on an undersized submain.
A Larger voltage drop will be fine for that kind of load yes, but will it be ok for the cable?
Don't forget that the voltage drop is just a product of resistances in series, the resistance of the cable being put in series with the load. So, as with any circuit of resistors in series, the greater the voltage drop across the resistor, the more power (as heat) is dissipated by it.
Obviously with an LED lighting circuit you wouldn't see any appreciable temperature rise in the cable in even an extreme case, but the rules have to cover all possible cases.