paulthemagpie

hi guys,

what would be a suitable wiring system for a three phase machines as an alternitive to the already proposed trunking and conduit system.

Am i right in saying SWA

thanks
 
SWA would be fine
 
If conduit/trunking is the proposed wiring/containment method mentioned in a contract specification, then you will need a change/Variation order to change!! You would need some solid and very good reasons to get that one past me...lol!!

For example, ...Why would i want to give up a wiring system that is adaptable and rewirable to future needs for a system that is NOT!!
 
thanks for the help guys and confirming that for me!

It was an assignment question, so i had to just propose another method!

thanks again
 
If that's 304 then I said "4 Core". Maybe that's a bit short.

I put MICC & FP200 for "suitable wiring for Fire Alarm." Any better answers?

Q1 was an pain wasn't it? Determine min mm[SUP]2[/SUP] of L conductors suitable for current & V drop, & min CPC of 4 different machines (1 & 3p) @ x°C grouped together. Took an evening of pencil sucking/page flipping to realise all I needed was Appendix 6 of Red OSG* All those tables...found 2 for ambient, but which one? Then realised significance of the different Appendixes, then realised I needed App. 6 & so it went on. To get I[SUB]f[/SUB] for the diabetic equation I divided 230V (for 1 & 3p) by Zs values in Table 41.3 BGB.

Dom.
(*Yeah we could flog my Red OSG to death.. or we could stay on point) :seeya:
 
dom i know exactly were you coming from!

what i havnt liked about this course so farwith my training company is the 301, 302, 303 is a load a health and safety and leglesation bollicks we are never going to know! they like 150 - 200 pages over them 3 first units of utter crap.

then when we come to the 304, they gloss over how to do important equasion and dont even explain what some the symbols means! Im fuming to be honest as im spending all my time on here trying to find answers.

yes question 1 was a hard one.

for B the min CSA on circuit protective conductor i ended up just referring to the BS7671 as they a table which states the min CSA of the cpc.

I tried working the equasions but my tutor would help me the *******. lol
 
yes question 1 was a hard one.

for B the min CSA on circuit protective conductor i ended up just referring to the BS7671 as they a table which states the min CSA of the cpc.

I tried working the equasions but my tutor would help me the *******. lol

Then when i get here the tutor saying he not allowed to give me any input.

What table was that Paul? For my own reference. Ta muchly.

You could say "I need 4mm cable for the machine so I need 4mm CPC" as per BGB* but I think they want you to use that anorexic equation to "determine the minimum size" of say, 0.44mm[SUP]2[/SUP] before you mention that. That is the important point. But yes "determine minimum size" could also be your answer.

This is an open-book test & you have to get 100%
As I understand it, you can ask your teacher & discuss with peers, in order to fully understand it & thus get 100%
If you don't get 100% I assume your teacher will explain your incorrect answers so you can understand it, answer it correctly & achieve 100% How else could you?

Dom.



PS !!! I really hope you tutor goes on & on about Block Diagrams as the most appropriate method of displaying how the distribution circuits for a large installation are arranged, as you can go on & on about schemetics, circuit diagrams, notices / labels @ the db/ site plans/ architects plans etc but you'll lose three points out of 35 (8.6%) if you don't use that magic word. Just like Risk Assessment question: You can bang on all day about them but if the word "hazard" isn't in there you screwed (good job I took a thesaurus in with me eh?)!!!



* I am sooo tired so if that's not quite right forgive me... CPC has to equal Line or not?
 