Hi all plastic pipes are run in a flat I am about to start . Only 300mm of copper is used to feed taps in bathroom and 900mm feeding boiler is s/ bonding needed as it is not clear in the on site guide thanks
 
Use your MFT on 500v, test between suspected extraneous conductive and MET , get a reading >23k ohms Dont bond, lower than 23k Bond it.

230 v/23000 ohms = 0.01 (10 milliamps).
 