Hi all. I have a question regarding a sub main which has a 80A rcd as the main switch which I was planning on supplying from a 63A mcb (im thinking bad practice) what's your thoughts?

Rgds

Sorry for type errors using my phone!
 
Last edited by a moderator:
Hi all. I have a question regarding a sub main which has a 80A rcd as the main switch which I was planning on supplying from a 63A mcb (im thinking bad practice) what's your thoughts?

Rgds

Sorry for type errors using my phone!

actually the opposite pal its fused down to 63A
 
the 80A rating of the RCD is the max. load it can safely handle. nothing to do with overload. so your plan is sound.
 
Only thing I would add is to check whether you really need a 63A supply, as the cable won't be cheap.
 