D
davesparks
Out of interest, why is it not best practice to run the outside feed from a FCU to a CU? The FCU is protecting the cable. Could there not be a case of installing a larger swa?
Remember I'm still new to this
By the way, why? I thought pretty much everything has to be RCD protected. I know there are exceptions
Creating a circuit which is both distribution and final circuit in one goes against common sense before you've even looked at the regulations,as does sharing a final circuit between a house and outbuilding.
Any fault or overload in the outbuilding could cause a loss of the final circuit in the house.
Feeding a CU from a 13A fuse is pointless, especially when the CU has an ocpd rated higher than 13A,
Whilst we all appreciate that you are new and none of us ever stop learning there is a basic level of knowledge and experience needed before you can safely go out on your own. It's not fair on a customer for them to think they are employing a qualified professional when they are actually paying for someone to practice and get their designs checked/reviewed by a bunch of strangers on a forum.
Some things require RCD protection but certainly not everything, RCD protection is generally an additional thing required for certain things. Socket outlets 32A or below and not for a specific documented purpose, TT systems, bathrooms etc require RCD protection. The only place that you would usually consider everything needing rcd protection as a blanket requirement is the domestic sector.