Out of interest, why is it not best practice to run the outside feed from a FCU to a CU? The FCU is protecting the cable. Could there not be a case of installing a larger swa?
Remember I'm still new to this

By the way, why? I thought pretty much everything has to be RCD protected. I know there are exceptions

Creating a circuit which is both distribution and final circuit in one goes against common sense before you've even looked at the regulations,as does sharing a final circuit between a house and outbuilding.
Any fault or overload in the outbuilding could cause a loss of the final circuit in the house.
Feeding a CU from a 13A fuse is pointless, especially when the CU has an ocpd rated higher than 13A,

Whilst we all appreciate that you are new and none of us ever stop learning there is a basic level of knowledge and experience needed before you can safely go out on your own. It's not fair on a customer for them to think they are employing a qualified professional when they are actually paying for someone to practice and get their designs checked/reviewed by a bunch of strangers on a forum.

Some things require RCD protection but certainly not everything, RCD protection is generally an additional thing required for certain things. Socket outlets 32A or below and not for a specific documented purpose, TT systems, bathrooms etc require RCD protection. The only place that you would usually consider everything needing rcd protection as a blanket requirement is the domestic sector.
 
It’s also rather pointless having a cu in the outbuilding with a 16A MCB if the origin has a current limit of 13Amp.
You are supposed to provide discrimination of protective devices.
Good point. Do you think in a situation such as this it would be reasonable to do away with the FCU, and have the whole outbuilding on a 16A breaker?
 
Good point. Do you think in a situation such as this it would be reasonable to do away with the FCU, and have the whole outbuilding on a 16A breaker?

No, doing away with the CU in the outbuilding and using a SFCU with 3A fuse for the light would be reasonable in my opinion.
 
It's not fair on a customer for them to think they are employing a qualified professional when they are actually paying for someone to practice and get their designs checked/reviewed by a bunch of strangers on a forum.
The client is actually a friend, who knows exactly where I am with regards to my current position. At no point have they been misled into thinking I'm anything other than what I actually am.
I appreciate some people out there would take everything said on the internet as gospel, however I assure you I'm not. I'm seeking people's opinions along side trying to work safely within the regulations.

basic level of knowledge and experience needed
I hope you can appreciate they didn't cover this scenario on either the 2365 lever 2 or 3, or the 18th edition, or the part P courses.
Creating an atmosphere of hostility can cause people to keep their heads down and not ask questions. This in turn can lead to mistakes being made, when if they had just asked 'the stupid question' it could have been avoided

Many thanks for your concern though.

Thank you everyone for your help and advice. I have learnt a bit more and you have helped clear the muddy water.

Look forward to picking you're brains again sometime
 