- Reaction score
- 13
Hi team.
A couple of questions for you.
Just to explain as well. I've just completed the level 2 & 3 diploma, and I'm now trying to work out in the big wide world.
All of this is in regards to a studio outbuilding. The outbuilding is located about 25 meters away from the house.
It is fed via a fused spur taken from a ring main. The ring main is protected with a 32 amp mcb, no RCD.
The feed cable is only 2.5mm 3 core SWA.
The feed goes to a CU in the studio which is RCD protected with 2 circuits, a light on a 6amp and radial on a 16a.
The studio is also on a TT
So firstly, is the general set up ok? To my limited experience it would seem so as the feed is protected so the cable is never going beyond is safe level with regards to current carrying capacity.
Secondly though is volt drop.
When I have worked it out, it seems to be well over the 3 limit for the lighting, but when tested against the inside of the house, there is basically no drop. The confusing part for me as well is the wording in the 7671. When it refers to the origin of the installation, do you take that as the tails into the main CU or the studio CU. The studio is an installation and is origin is there.
Many thanks as always team