cliffed

-
Arms
How come some qualified electricians will argue & argue about earthing the armouring of the cable.
Seen many jobs where they use plastic junction boxes & no earth continuity on the armouring.
Regardless of how many cores are used it still needs earthing.
Their biggest argument is it’s only for mechanical protection are they actually taught this @ College
 
It's a no brainer, it has to be earthed. There's no 2 ways about it. If it's only for mechanical protection it still has to be earthed to prevent the scenario where the armour becomes live due to damage to the cable.
Exactly my external lights had Swa cabling to them I used 4c ….2Years later fault on the lights… 1core down to earth tripping Rcd….manage to reconfigure connections.
The guys had put hardcore then used a Wacker…most probably a stone had pierced the sheath & armouring then the cable.
Embarrassing I must say…sparky fault on his lights.
Had a go @ builder …he said you must of put a faulty cable in…😂😎
 
Much of the time the armour is being used as the cpc anyway so it should be habit to earth it.
Tbh I've only just recently started using the armouring as the CPC. Used to always get 3core or 5core rather than 2core or 4core.

Company I worked for as an apprentice always did it that way so it was habit for me to do the same when I started to get the materials myself.
 
Firstly we assume we are discussing low voltage here and not extra low, if that is the case then the armouring must be earthed with no exceptions however depending on there been a separate earth core then that would denote if you only earth one end or both, if separate earth core then one earthed end is fine on armouring and good practice is at the supply end not the load to reduce fault current times and the vulnerability of load ends been more subject to wear and tear and alteration, although no regulation specifies this as inspections should routinely check all this.
 
Last edited by a moderator:
There are also permutations of sizes and cores where the copper equivalent size of the steel isn’t up to scratch to use the armour as a cpc.
I think going back to first principles of ADS and fault protection for the distribution circuit and anything downstream is wise before assuming it’s ok to do this.
 
Firstly we assume we are discussing low voltage here and not extra low, if that is the case then the armouring must be earthed with no exceptions
Absolutely!
however depending on there been a separate earth core then that would denote if you only earth one end or both, if separate earth core then one earthed end is fine on armouring and good practice is at the supply end not the load to reduce fault current times and the vulnerability of load ends been more subject to wear and tear and alteration, although no regulation specifies this as inspections should routinely check all this.
There are possible corner cases when the armour is not a low enough R2 on its own to meet disconnection times and/or fails adiabatic, then having a good copper CPC linking both ends will make sure that a cable L-armour fault is safely disconnected. In that case you could find regulations that demand it!
 
I'm fully aware of that but usually that is out of the scope of general chat on here and only needs mentioning if relevent, no one mentioned sizing and cores in the 120mm etc, with all respect if they are fitting them at that size then you expect some level of knowledge of said regulations.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Swa armouring let it be Earth
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
cliffed,
Last reply from
Darkwood,
Replies
15
Views
2,098

Advert

Back
Top