Engineer54
"But having said that I will agree that after reading that i would need to start fitting banjo's or earth nuts in the future".
Yup.
At both ends mate with a 6mm brass nut and bolt either tapped or drilled through the banjo and box(paint removed with file and contact grease applied of course lol).
You then take a fly lead from the 6mm bolt and armouring to the internal earthing terminal of the board...........sized accordingly.
You then have your internal earth as your cpc and your swa as a cpc(if required) and they can then both be a bond and vice versa.............complimenting each other as it were
Then you have the parallel paths and disconnection times in a nano second.......................................................
Or you can just use the Swa as your cpc of course![]()
That statement isn't actually correct. If there is a 3rd core being used as the circuits CPC, then the SWA armouring isn't classed or considered as a CPC at all, it'll just be an earthed exposed conductor, that only needs to be earthed at one end of the cable. You should never rely on two different metals being used as a single or combined CPC, as any fault current will NOT be shared equally between the two differing metal conductors!!