Sorry about the delay in responding to your further queries - was called away.
The cores provided a ring circuit with red (live) and black (neutral) with the return being yellow (live) and blue (neutral) with the armour providing CPC. We moved in a couple of months ago and have not used the garden room - I plugged in a fan and it tripped.
On testing the cores and the armour there is continuity in all but the yellow core. I have tested the IR and that is good although not clear - reading 140 mohms - used a Megger MFT.
My thoughts are to convert to a radial and reduce the protective device from a rating of 32A to 16A.
I recon that its unlikely to be a broken yellow core in the cable but disconnected at one of the terminals somewhere,
Light blue touch paper and stand well back ......... Whoosh