nice trolling , touche lol.
Think i'll leave the Trolling to you, that's your dept after all!! I don't want to step on anybodies toes. ...lol!! :teeth_smile:
6.9v....why are you looking at cables that give you a 11v voltdrop ?
it needs to be below 6v volt just for your lighting anyway ?
Cant do the calcs for you without an ib , but i would imagine the cable will be no less than 95mm even for a smallish load.
Anyone who can afford the land and to build stables on it can pay for it to be done properly , end of.
6.9v....
Sorry unless im being a numpty 5% voltdrop allowed for power at 240V thats 11.5 volts and the amps watts ive calculated with would be the max load permitted that falls within the 5%.
I would have thought you have to calculate power as its a shed supply so will be both and thats the worse case.
Am i way off then?
@FCC5206.... Gonna have to be a bit blunt here but dont take it as a dig.
Reading through im aware your customer is not forthcoming with info but you have been told its a 2bed house to design for so rather then throwing random 100amp figures out there try be more realistic and lets say an 18KVA supply would be adequate for your average 2up 2down.
You expect to run this off an existing house which may have a DNO fuse as low as 40amp that we can't know without enquiry and can't thus understand why such a large supply is been thrown in unless it can be confirmed the house could have a larger supply fitted at a future date. Has anyone even discussed an upgrade as well as existing fuse size with the DNO?
If the possibility of running this cable is an option for future plans then also to think about is metering as it will be on the first property and if planning permission is given then building a 2 bed house will always be tagged to house one, its unlikely the DNO will adopt your cables you have run to loop off house one and meter house 2 individually... this will be a big issue for a sale if that's the plans ever.
So before even putting calculation to paper firstly get all the relevant info to see if its practical or just a waste of money putting this larger cable in. Your customer is the ill educated one and irrespective of there demands and preferences if you present the case that this is throwing money away you will gain a lot of respect and a good name.
Apologies if ive missed info already supplied so ignore any comment if the case but i got brain mash with all the street lighting trolling crap :banghead:
Edit to note here is the possibility that if house is built that heating maybe electric as i assume no gas exists down there either and will have to be put in at great cost.
youre looking at this the wrong way...
theres no point thinking along the lines of 35mm for 7.2kw , 50mm for 9.6 etc etc.
the real questions that need answering have nothing to do with cable calc and volt drop..........
what does the customer want to achieve ?
what are his budget limitations ?
is he aware of the realistic costs involved and design criteria that need to be met ?
factoring in spare capacity for the cable in the off chance he may want to expand in the future will add massive initial materials costs , does he want this ?
unless he can answer all of these questions convincingly then i wouldnt spend any time designing a submains for someone who just wants a cheap bodge.