i still expect an answer to the very basic (and reasonable) questions i asked at #7...
your response at #11 is not acceptable...
 
bgb is in van currently locked in garage as too many people round here seem to think a van is a free cash machine, hence the ball ache to go get it,
 
Well as you are the one designing a circuit, the BGB should be in your hand! People pay me good money to design circuits for them!

Go fetch!
 
bgb is in van currently locked in garage as too many people round here seem to think a van is a free cash machine, hence the ball ache to go get it,
well...
in all fairness you dont need a book to know the answers i posed to you at #7...
 
James...
if its a 2 core....
and theres no evidence of any TT having been there (you can always ask the customer this)...
then what do you think has been serving as the earthing for the recently deceased garage
 
come on james...
out with it man..

- - - Updated - - -

if you answer and its incorrect....
we will then be prepared to guide you...
 
i am now looking at book ( albeit through red wine tinted glasses) please correct me if the line i am thinking covers me is wrong

a protective conductor may consist of one OR more of the following ...
a metal covering, for example the sheath,screen or armouring of a cable.

therefore i am assuming that i can use the sheath in accordance as long as its equivalent csa meets the minimum

i now see glenn that i can use the steel conduit, as for the three phase i cannot honestly answer that question, i have only ever worked in domestic field
 
i am now looking at book ( albeit through red wine tinted glasses) please correct me if the line i am thinking covers me is wrong

a protective conductor may consist of one OR more of the following ...
a metal covering, for example the sheath,screen or armouring of a cable.

therefore i am assuming that i can use the sheath in accordance as long as its equivalent csa meets the minimum

i now see glenn that i can use the steel conduit, as for the three phase i cannot honestly answer that question, i have only ever worked in domestic field
correct.

now, whats the matter with that 3 phase motor?
 