k guys needs some advice,

We have an event on tomorrow and we been asked to run 100m of 4mm sy cable to power up the event.

Now I know have mixed options but can this be done or should it be run in SWA cable??

The cable will be protected by 32amp in a splitter box

Cheers guys
 
Last edited:
Well 4mm is 11mV per A per m. I’ll let you multiply it out :) .
Depending on actual loading I think you’re going to need 10mm or more. Why not use SWA?
 
It will either be SWA or Hi Tuff. And 4mm will not be sufficient, even with diversity you will be looking at a minimum of 16mm.
 
100m is a long distance.
How will the cable be run for this event?
How are you protecting it?
 
Cheers

They think sy is totally acceptable and say it an be used in running three phase power,

Cheers guys for feedback.

How do 'they' intend to run this cable?
How are 'they' going to protect it from damage?
 

Reply to Sy cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
339
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
27
Views
460
Hi all, Interested in the groups interpretation of BS7671 with regards to the used of SY & YY cables. We have a commercial installation where we...
Replies
8
Views
2K
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
853
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock