Discuss Sy cable in the UK Electrical Forum area at ElectriciansForums.net
k guys needs some advice,
We have an event on tomorrow and we been asked to run 100m of 4mm sy cable to power up the event.
Now I know have mixed options but can this be done or should it be run in SWA cable??
The cable will be protected by 32amp in a splitter box
Cheers guys
Well 4mm is 11mV per A per m. I’ll let you multiply it out :) .
Depending on actual loading I think you’re going to need 10mm or more. Why not use SWA?
It will either be SWA or Hi Tuff. And 4mm will not be sufficient, even with diversity you will be looking at a minimum of 16mm.
100m is a long distance.
How will the cable be run for this event?
How are you protecting it?
Cheers
They think sy is totally acceptable and say it an be used in running three phase power,
Cheers guys for feedback.
How do 'they' intend to run this cable?
How are 'they' going to protect it from damage?
Reply to Sy cable in the UK Electrical Forum area at ElectriciansForums.net
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Hi all, Interested in the groups interpretation of BS7671 with regards to the used of SY & YY cables. We have a commercial installation where we...
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...