Hi,

I've been called to a job where the kitchen extension lights are on the same circuit as the rest of the downstairs lights, but between the switch for the hall lights and the switch for the kitchen lights there seems to be a break in the cpc, because the cpc at the kitchen switch and all of the kitchen downlights is showing a voltage, presumably from induction.

If I connect a wire between the cpc at the hall switch and the cpc at the kitchen switch it clears the voltage. The circuit is run with line and neutral to the switches, not the lights, and cabling for both switches run up to the ceiling above which is a flat roof so no access from above. The customer has just had the ceiling done and doesn't want to have chunks of it pulled down to find what I'm guessing is a junction box with a cpc popped out of it. I did an IR test L/E and N/E at both switches which was fine.

My question is, would I be able to, as a permanent workaround, run a 4mm single cpc between the two switches, as this would make all points on the circuit protected, and leave the break in the cpc where it is?

Thanks.
 