It's been an interesting thread. It's slowly emerged that there seems to be a well engineered distribution circuit and the fact it was a "ring" got slightly overlooked at first as the very logical reaction was 'that's more than 20 amps so of course it will trip'.
Those commenting at the beginning didn't know there was a 10 sq mm SWA feeding it and it initially sounded like a cheap and nasty job.
To my thinking there are two definite things to check before changing that device:
-Is the Zs low enough for a B32? If not it would rely on RCD technology to turn off in time under fault conditions, and a new certificate needs to state that RCDs are being employed for fault protection. (If moving to a type C then even more reason to check this).
-Do end-to-end tests confirm it's a healthy ring final circuit and is eligible to be protected by a 32 amp device in the first place?
I'd also want to know the OCPD of the distribution circuit, it might be 25 amp MCB for all we know and the problem just moves. Unlikely, but possible!
It comes down to a simple choice
-stick a B32 in and hope all is ok
-get 5 minutes of testing done and be sure all is ok.
Those commenting at the beginning didn't know there was a 10 sq mm SWA feeding it and it initially sounded like a cheap and nasty job.
To my thinking there are two definite things to check before changing that device:
-Is the Zs low enough for a B32? If not it would rely on RCD technology to turn off in time under fault conditions, and a new certificate needs to state that RCDs are being employed for fault protection. (If moving to a type C then even more reason to check this).
-Do end-to-end tests confirm it's a healthy ring final circuit and is eligible to be protected by a 32 amp device in the first place?
I'd also want to know the OCPD of the distribution circuit, it might be 25 amp MCB for all we know and the problem just moves. Unlikely, but possible!
It comes down to a simple choice
-stick a B32 in and hope all is ok
-get 5 minutes of testing done and be sure all is ok.