J
johnboy6083
For a ring you work out Ib and multiply this by 1.67 to get your protective device. This is In. You then find It, by dividing Ib by the derating factors (Cg, Ci, Cg, Ca and finally 0.725 if a 3036 fuse).You then have a provisional conductor size. Check this with the following, max mv/a/m = max vd/ (length x Ib). You look down the tables and find a conductor with a mv/a/m figure less than this. You then need to check thermal withstand and disconnection times. You also need to select or calculate a CPC.