I am undertaking a complete refurb of my property including a relocated meter & new relocated CU.

I discussed my requirements with a qualified electrician who advised me that as the new location for the CU is more than 2 meters from the meter and is being located at the top of a new stud wall that a 80amp breaker will need to be installed in the meter cabinet and the tails which are going under the floorboards - raised floor - and up inside the stud wall to the CU need to be installed inside a steel conduit. This was all completed and the electrician connected the tails to the CU and provided a working socket to allow power in the property to continue the refurb.
The electrician has now advised me that he is unable to do any more work for me as he has taken a full time job with a electrical company.

I have subsequently contacted another qualified electrician who has advised that the installation is incorrect as the tails should be in plastic conduit not metal for 2 reasons -

1. If anybody drills a hole in the stud wall and drills through the steel conduit into the live tail the conduit will become live.
2. As the live and neutral are both in steel conduits and are running alongside each other from the meter to the CU - eddy currents will be formed and the tails will overheat.

Who is correct ???
 
Hi RBPMS i dont think your new electrician is right as i think the tails will be much safer in steel conduit then in a plastic conduit, if he is worried about the steel conduit becoming live why does he not just earth the steel conduit (and place a fused isolator just before it goes into the steel conduit so that if it was to become live it would not trip the main dno fuse) that would make sure if it did come live it would trip trip and become safe.

As for the eddy currents that is not true at all as live and neutral cancel each other out so no eddy currents would occur.

-------edit--------

just notice that u said there was a 80amp breaker in the coubard with is what i suggested should be installed sorry its a bit late haha
 
I would think the first one as plastic conduit offers no mechanical protection.I would also expect the metal conduit to be earthed.

Beat me to it Mr Baker.
 
Is the stud wall metal or wood?
location of the consumer unit in the middle of the wall or off to a left or right side?(safe zones for running cabling)

They are both correct in there way of thinking. Both the line and neutral should be in the same metal enclosure. If the steel conduit is fitted it will be earthed to the install so the conduit becoming 'live' should not be an issue.
 
Are you really the customer of an armature spark looking for free information?

There are major problems with the set up you describe, but I would suggest you get someone qualified in.
 
Thanks for your information guys - Tony as I mentioned both the electricians mentioned in my post are qualified - I'm doing 1st fix - they are doing second fix & certification.
After posting my question I searched for "eddy currents" on this forum and having read a lot of differing opinions - why is nothing simple in electrics - it appears that if the live & neutral tails are in the SAME conduit - no problem - however if they are in seperate conduits running alongside each other there could be potential eddy current issues.
I was just wondering how far apart the two conduit runs need to be to eliminate eddy currents ? Currently both the flexible galvanise conduits runs along the same side of a 100 x 50 floor joist then up the same side of a 100 x 50 timber stud to the CU which is located at the top of the stud.
If I moved either the live or neutral to the other side of the floor joist and the other side of the wall stud would this prevent eddy current ?
Have paid out for 20 metres of 25mm flexible conduit don't really want to have to replace it with larger diameter to house both live & neutral.
 
It doesn’t matter how far apart you move them they will still be in the separate conduits. It is this that causes eddy currents.

Get some one in that knows what they are doing.
 
Thanks for your information guys - Tony as I mentioned both the electricians mentioned in my post are qualified - I'm doing 1st fix - they are doing second fix & certification.
After posting my question I searched for "eddy currents" on this forum and having read a lot of differing opinions - why is nothing simple in electrics - it appears that if the live & neutral tails are in the SAME conduit - no problem - however if they are in seperate conduits running alongside each other there could be potential eddy current issues.
I was just wondering how far apart the two conduit runs need to be to eliminate eddy currents ? Currently both the flexible galvanise conduits runs along the same side of a 100 x 50 floor joist then up the same side of a 100 x 50 timber stud to the CU which is located at the top of the stud.
If I moved either the live or neutral to the other side of the floor joist and the other side of the wall stud would this prevent eddy current ?
Have paid out for 20 metres of 25mm flexible conduit don't really want to have to replace it with larger diameter to house both live & neutral.

Good luck getting that signed off.

I wouldn't sgn it off and neither should ANY respectable member of a scheme.

Sounds like you are on your own pal.
 
On a job like this, why on earth do the electricians make it so difficult and decide to start trying to run tails in conduits?

What the hell is wrong with using SWA? Is it just me who would do it this way or what.
 
On a job like this, why on earth do the electricians make it so difficult and decide to start trying to run tails in conduits?

What the hell is wrong with using SWA? Is it just me who would do it this way or what.

Because lazy and ill-trained 'sparks' don't have the basic skills to handle armoured, basically.
 
Because lazy and ill-trained 'sparks' don't have the basic skills to handle armoured, basically.


From what i've seen and read on these forums, many don't even have the basic skills to work/handle T&E!! But still deemed competent by the safety conscious scheme providers!! lol!!
 
I’ll admit, running singles in individual conduits is one of the better ones seen on here. Original in the OP’s thinking.






Now to chuck a spanner in the works, in theory there is a way to run singles in individual conduits. It took one of my friends at Mumbai University to come up with it. It started with a hypothetical question.

This is PURE theory though. Being retired I no longer have the facilities to test it. Given half the chance I would, wouldn’t be the first time I’ve set fire to something!

Eddytheory_zps8aa6035b.jpg


In theory the induced circulating current in the earthed loop should cancel the line and neutral currents.

I love theory!
 