I am undertaking a complete refurb of my property including a relocated meter & new relocated CU.
I discussed my requirements with a qualified electrician who advised me that as the new location for the CU is more than 2 meters from the meter and is being located at the top of a new stud wall that a 80amp breaker will need to be installed in the meter cabinet and the tails which are going under the floorboards - raised floor - and up inside the stud wall to the CU need to be installed inside a steel conduit. This was all completed and the electrician connected the tails to the CU and provided a working socket to allow power in the property to continue the refurb.
The electrician has now advised me that he is unable to do any more work for me as he has taken a full time job with a electrical company.
I have subsequently contacted another qualified electrician who has advised that the installation is incorrect as the tails should be in plastic conduit not metal for 2 reasons -
1. If anybody drills a hole in the stud wall and drills through the steel conduit into the live tail the conduit will become live.
2. As the live and neutral are both in steel conduits and are running alongside each other from the meter to the CU - eddy currents will be formed and the tails will overheat.
Who is correct ???
I discussed my requirements with a qualified electrician who advised me that as the new location for the CU is more than 2 meters from the meter and is being located at the top of a new stud wall that a 80amp breaker will need to be installed in the meter cabinet and the tails which are going under the floorboards - raised floor - and up inside the stud wall to the CU need to be installed inside a steel conduit. This was all completed and the electrician connected the tails to the CU and provided a working socket to allow power in the property to continue the refurb.
The electrician has now advised me that he is unable to do any more work for me as he has taken a full time job with a electrical company.
I have subsequently contacted another qualified electrician who has advised that the installation is incorrect as the tails should be in plastic conduit not metal for 2 reasons -
1. If anybody drills a hole in the stud wall and drills through the steel conduit into the live tail the conduit will become live.
2. As the live and neutral are both in steel conduits and are running alongside each other from the meter to the CU - eddy currents will be formed and the tails will overheat.
Who is correct ???