What is this hysteria about tails in a cavity,my goodness, if they needed changing would some of you butcher a wall to chase them,surface trunking them or even sling in some surface mounted swa?

If so it seems that a reality check is on the cards if you think the remote possibility of a cavity bridge is better considered than doing what has been a standard tails installation method for eons
 
What is this hysteria about tails in a cavity,my goodness, if they needed changing would some of you butcher a wall to chase them,surface trunking them or even sling in some surface mounted swa?

If so it seems that a reality check is on the cards if you think the remote possibility of a cavity bridge is better considered than doing what has been a standard tails installation method for eons

You may have a point. Could be one of those things people are just told with no substance. Does anyone actually have a reg for this?
 
There is no prohibition in BS7671 against running cables in the cavity.
In fact BS7671 specifically allows building voids to be used.
However the DNOs do not like it, as they believe there is the possibility of damage caused by debris falling inside the cavity.
 
However the DNOs do not like it, as they believe there is the possibility of damage caused by debris falling inside the cavity.

So how do they expect us to get our tails inside from a external meter cupboard?

SWA seems a little excessive for a short run through a wall.
 
There is no prohibition in BS7671 against running cables in the cavity.
In fact BS7671 specifically allows building voids to be used.
However the DNOs do not like it, as they believe there is the possibility of damage caused by debris falling inside the cavity.

Many of the circumstances of using the cavity i've seen, were actually instances where the DNO's (or should i say the old Regional Electricity Boards) had used the cavity. These mainly on overhead supply systems where they had actually requested a pull wire/cord to be installed by the builders, on new builds of the time.
 
Isn't the trend now for most cavities to be filled with insulation of one kind or another, so that the only thing that can call onto the cables is bits of lightweight insulation?
 
and in that case, tails would need to be derated, maybe by up to 50%. that'll be fun, fitting 70mm tails.
 