Extra checks needed for a BS 8436 Cable
When the basic overload relationship (above) is applied, virtually all cables are protected from damage by the fault current. However for BS8436 cables, contractors or designers must either read BS8436 in detail or follow the following advice when installing a BS 8436 cable concealed in a wall or partition.
The following guidance is relevant for 1.0mm, 1.5mm2 and 2.5mm2 cables only.
1. The cables shall only be used in circuits protected by a type B circuit breaker to BS EN 60898 or type B RCBO to BS EN 61009 with a rating not exceeding16A, 20A or 32A for cable sizes 1.0mm2, 1.5mm2 and 2.5mm2 respectively.
In both cases the circuit breaker must be energy limiting class 3.
This is because only these protective devices have a maximum current needed to operate them which does not exceed 80A, 100A and 160A in a time of one second, for cable sizes 1.0mm, 1.5mm and 2.5mm respectively, and the let through energy is such that it will not thermally damage the cable.
2. The prospective earth fault current in the circuit does not exceed 5,000A. (This corresponds to an earth fault loop impedance (ZS) of not less than 0.048 ohms