So if the cable carrying capacity is less than 60amp I'm sound anything over then an upgrade is required?? Just to clear things up cheers for help guys.

It's no different to working out the cable size for a final circuit. If you know the CCC of the tails, and that it is protected by an appropriately rated fuse, then you're good to go!
 
The OSG insist on 25mm tails.. But remember this is a guide.. check cable carrying capacity for size of tails and that decides wether your tails need upgrading or not

They show 25mm tails,but remember that the OSG is aimed at new installs..... if it covered all the types of installs over the years it would be as big as the encylopedia britannica
 
So if the cable carrying capacity is less than 60amp I'm sound anything over then an upgrade is required?? Just to clear things up cheers for help guys.

From memery im sure 16mm tails are good for 80 ish amp.. Providing main fuse is 80 or less and tails are in good nick then why upgrade?
 
Cheers lads helped me out no end appreciate it. This forum is perfect for new starters like to t get advice from your more experienced lads cheers
 
Cheers lads helped me out no end appreciate it. This forum is perfect for new starters like to t get advice from your more experienced lads cheers 

Another happy customer, would it trouble you to fill out a quick feedback form on your experiences of the forum today? Only joking ;-)
 
The main tails are prob 16mm because the fuse is 60/80.
The fuse is 60/80 because that is the rating of the tele switch (guessing it doesnt say 100a on it)
 
It must depend on the DNO. I called out EDF to change meters (customer had economy 7 meters and didn't want that tarrif), I had installed new CU with 25mm tails to old meter, 60A fuse, when I returned they had also changed their old 16mm tails from head to 25mm. I was surprised they even changed the meter, let alone the tails!
 
It must depend on the DNO. I called out EDF to change meters (customer had economy 7 meters and didn't want that tarrif), I had installed new CU with 25mm tails to old meter, 60A fuse, when I returned they had also changed their old 16mm tails from head to 25mm. I was surprised they even changed the meter, let alone the tails!
they may have changed the bullit...
 
I was told by elecsa that all tails on ccu upgrades (domestic) must be 25mm no matter what size fuse. Which I think is a bit silly on small flats or houses.
 