I have a job coming up the week after next where I have to terminate a 50mm solid core incomer into a Schneider standard 125A single phase main switch in an acti 9 board.

The plan I have come up with is to get the little adaptors Schneider make to allow a lugged connection to be made to the main switch, this bit I'm happy with.
But then all I can think of to actually fit the lug to the conductor is to find the closest matching lug and sweat it on.
Whilst I am capable of doing this I would appreciate any suggestions that don't involve hot works permits, fire alarm isolation and the perceived risk of setting fire to an old, well known and listed west end theatre!
 
Open any windows and cling film over the sensors are my two (rubbish!) pearls of non wisdom! A RA and a extinguisher by your side maybe....
 
Is it acceptable to crimp the lugs on? I do it often with 8mm diameter (50mm CSA) solid copper conductors but this isn't for electrical connections which is why I ask.
 
You can buy specific crimps and dies for solid core conductors. Just ask at a decent wholesaler and I'm sure they would be able to rent you the crimper.
 
I have a job coming up the week after next where I have to terminate a 50mm solid core incomer into a Schneider standard 125A single phase main switch in an acti 9 board.

The plan I have come up with is to get the little adaptors Schneider make to allow a lugged connection to be made to the main switch, this bit I'm happy with.
But then all I can think of to actually fit the lug to the conductor is to find the closest matching lug and sweat it on.
Whilst I am capable of doing this I would appreciate any suggestions that don't involve hot works permits, fire alarm isolation and the perceived risk of setting fire to an old, well known and listed west end theatre!

Hi

Copper or Aluminum Dave?

Cheers
 
I've used the Klauke products from the following range on round conductor and been happy with the results:
Tubular cable lugs from copper, for solid conductors, 6 - 50 mm²

One weakness with using conventional crimp lugs on solid cable is the CSA of the lug tube material can be rather small, making it mechanically flimsy relative to the cable. BICC Burndy used to make a special lug for solid with a collet chuck that tightened onto the cable with a pair of spanners. Haven't seen them for years, I guess they were ridiculously expensive to make.
 
I don't have any experience with solid conductors of this size at all so forgive me if this sounds naive or daft.

I have noticed in the past that such devices to 60947/60898 usually state a maximum terminal capacity for copper conductors of 35mm stranded and 50mm solid. Would it be at all possible to make a good connection directly into the terminal ? I have no idea of the malleability of a conductor of this size or whether the correct purchase could be gained. I assume it would have to be pre formed in some way to fit the terminal properly.
My instincts say no, but would there be an acceptable method of direct connection if the terminals are rated for the size ?
 
Hi

If its copper, then just crimp, i wouldn't solder, its actually more problematic. You have two options, use a din compression lug with a din compression tool, these can be hired. Or use a copper tubular lug and a good indent crimp tool.

Cheers
 
Lucien is on the money,Klauke make and supply the kit for this job. Their catalogue used to have the tools and fittings,together with the relevant methods and approvals.

I think the number of outfits hiring out expensive kit such as this,would be few...but it is great gear.

I was approached,a while back,by a company venturing in to the induction heat-gun market. These are 230/120V powered devices,used for jobs previously requiring a blow-torch,or oxy/propane gear,such as freeing fastenings and soldering.

If you need a hot-works ticket for soft/hard soldering 280-650 degrees,then really,you should require one for your cordless,with a blunt bit,that could get to 1300+...if not,the induction tackle may be the future...:army:
 
Lucien is on the money,Klauke make and supply the kit for this job. Their catalogue used to have the tools and fittings,together with the relevant methods and approvals.

I think the number of outfits hiring out expensive kit such as this,would be few...but it is great gear.

I was approached,a while back,by a company venturing in to the induction heat-gun market. These are 230/120V powered devices,used for jobs previously requiring a blow-torch,or oxy/propane gear,such as freeing fastenings and soldering.

If you need a hot-works ticket for soft/hard soldering 280-650 degrees,then really,you should require one for your cordless,with a blunt bit,that could get to 1300+...if not,the induction tackle may be the future...:army:

The issue is more that the heat source would be a naked flame cos a blowtorch is all I have for sweating it with
 
I don't have any experience with solid conductors of this size at all so forgive me if this sounds naive or daft.

I have noticed in the past that such devices to 60947/60898 usually state a maximum terminal capacity for copper conductors of 35mm stranded and 50mm solid. Would it be at all possible to make a good connection directly into the terminal ? I have no idea of the malleability of a conductor of this size or whether the correct purchase could be gained. I assume it would have to be pre formed in some way to fit the terminal properly.
My instincts say no, but would there be an acceptable method of direct connection if the terminals are rated for the size ?

The terminals are rated for the size, but there is a bit of a back story.
The job is basically to get rid of a ridiculous joint box where the 50mm MI joints to singles (2.5mm) which feed the 2way board with just the one 16A mcb in it.
So moving the board 6" along the wall and terminating the cable directly into it, but the bloke who is responsible for this abortion has told my customer that it's impossible to put the solid cores direct into the terminals because it'll burst into flames through poor connection (at 16A on a 50mm I could file the conductor flat to fit the terminal better and still it wouldn't get warm!)

This customer is one of those rare ones who always pay before the invoice due date, never question a quoted price and prefer to pay for quality over quantity, so I am more than happy to go the extra mile to keep them happy.
 
I've used the Klauke products from the following range on round conductor and been happy with the results:
Tubular cable lugs from copper, for solid conductors, 6 - 50 mm²

One weakness with using conventional crimp lugs on solid cable is the CSA of the lug tube material can be rather small, making it mechanically flimsy relative to the cable. BICC Burndy used to make a special lug for solid with a collet chuck that tightened onto the cable with a pair of spanners. Haven't seen them for years, I guess they were ridiculously expensive to make.

I've seen a lug which appears to just knock on and wedge in place in an old bicc book about micc, but assume such things are long gone.

What I'd like to see is something like a lug which attaches via set screws for this sort of thing, like those mechanical through connectors with shear bolts, but a lug.
 
They look like a way round the problem,probably quite expensive...BEFORE they tell you there only in bags of ten!

Hi

Im not so sure they are, are they suitable for class 1 Cu cable, i don't think they are, solid Al yes, not solid Cu. Crimping is the best way, leaves very little in the way of air gaps. Use a Din compression lug and tool, or tubular lug with good indent tool. Klauke do both, also with tubular they have two variations L and R, R having a very high copper content.If you are concerned, RS do temp stickers, wrap around at termination, pretty acurate.

Cheers
 

Reply to Terminating 50mm solid conductor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
805
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hello everyone, I’m based in the ROI and live in a rural location. Yesterday evening my electricity supply started to switch on and off randomly...
Replies
2
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock