I was not paying a lot of attention when writing the above posts, but I should say I was defining the minimum standards required for new work, it is always possible, perhaps preferable to work to a higher standard and that would extend to testing of the entire circuit to ensure compliance of your addition.
However business pressures often limit you to the minimum possible standard.
 
shirley, if you are taking a Zs reading from the new light you have added at end of circuit, then that reading applies to the whole circuit.
 
As previously mentioned, you would need to determine the suitability of the existing circuit in the first place. This requires a visual inspection of the cable (where possible) plus the suitability and operation of the protection device, the cpc, the line conductors and the adequacy and reliability of the earthing arrangement . So you would have to do some testing anyhow. Whether there is a requirement or not to record these tests on a minor cert it would be good practice to do so. The more information you can provide the better. As Richard says minimum standards are a requirement, but working to higher standards would be preferred.
 
or Crabtree.