I
Ian1981
Of course you can calculate your R1+R2 at design.Agree But you also don't calculate R1+R2 and design stage either , you calculate Zs from by inquiring what the Ze will be and adding that your R1+ R2 readings, As others have said you can't back calculate the R1+R2 but I believe loads sparks who do it, As for the ops question, I do all the test except Zs which I calculate .
It’s not what I would record on the EIC as I would measure it during initial verification however when deciding what cables to use then using the mv/a/m values at 20 degrees and multiplying by 1.2 will give me a ball park figure of design, added to the Ze I can see what my Zs should be for compliance with disconnection times