Basically its the company you work for who decides what type of installation/materials that are used ,but if the test results don,t add up you,ll be putting an extra cpc in

yours benji
 
yes i work for a company but i order the materials and installation is designed by electrical designers who always air on the side of caution by uprating cpc size. Some people are not up for change and again test results are all within max values.
 
Tested containment at various points of install and all results were under 1 ohm so ok . RCBO s installed on ring mains and many parrallel earths so all good. Containment i suppose is primarily for mechanical protection. scotty
 
When i did my apprenticeship in the 80's,i was taught that lockrings/locknuts were only used on runners and all the joints were painted with galvanised paint.
 
Tested containment at various points of install and all results were under 1 ohm so ok . RCBO s installed on ring mains and many parrallel earths so all good. Containment i suppose is primarily for mechanical protection. scotty


you suppose?? interesting answer On old PME systems the conduit /trunking was the earth a lot of those installations dont have RCDs so its vital you have a decent earth throught the metalwork, under 1 ohn isnt a very good reading there is it capain? it has to be a lo under near 0.05 ohms.

Dont rely on rcds as a get out for bad installs and desighn they are SUPPLIMENTARY fault protection.
 