scotsparky

~
Arms
Apr 11, 2009
1,874
211
1,638
Glasgow
I known this may start a debate however its a good question.

I have just had a look at Mr Marks Sparks install in the "Show us your installs " tread and notice a difference. When i served my time in Scotland we had to put a lockring at every coupling,conduit joint. However i noticed mr MarkSparks had none on his conduit. Is this an English thing and if so why??
 
Tested containment at various points of install and all results were under 1 ohm so ok . RCBO s installed on ring mains and many parrallel earths so all good. Containment i suppose is primarily for mechanical protection. scotty


you suppose?? interesting answer On old PME systems the conduit /trunking was the earth a lot of those installations dont have RCDs so its vital you have a decent earth throught the metalwork, under 1 ohn isnt a very good reading there is it capain? it has to be a lo under near 0.05 ohms.

Dont rely on rcds as a get out for bad installs and desighn they are SUPPLIMENTARY fault protection.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

scotsparky

Arms
~
Joined
Location
Glasgow

Thread Information

Title
The Scotland England difference
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
21
Unsolved
--

Advert

Thread statistics

Created
scotsparky,
Last reply from
captainconduit,
Replies
21
Views
5,952

Advert