What about medical ? Emergency lighting, Alarms ?.
I can see that there is an argument for SPD on say, mains powered linked smoke alarms (and medical, alarms etc). But you are far more likely to have a power failure which renders smoke alarm system inoperable than you are a surge. So for the SPD requirement to make sense, a UPS needs to be mandated. Mission critical systems always have a UPS and just putting an SPD on is a waste. That of course will come in later iterations of the regs....but for now it ain't there !
 
I can see that there is an argument for SPD on say, mains powered linked smoke alarms (and medical, alarms etc). But you are far more likely to have a power failure which renders smoke alarm system inoperable than you are a surge. So for the SPD requirement to make sense, a UPS needs to be mandated. Mission critical systems always have a UPS and just putting an SPD on is a waste. That of course will come in later iterations of the regs....but for now it ain't there !

If you don't mind my asking - what edition of BS7671 are you referencing?

The problem for electricians is that, while many domestic installations may not benefit much from the addition of surge protection, its omission is no longer a matter that can be settled by a customer simply declining the option and now requires a risk assessment. A comprehensive risk assessment takes a significant amount of time, for which the designer will receive no compensation, whereas inclusion of surge protection adds minimal cost to an installation. If you were designing installations, would you take the time to write up a risk assessment for every individual, in many cases finding yourself unable to remove the requirement of surge protection, or would you include it as part of the specification and save yourself considerable hours of unpaid work?
 
If you don't mind my asking - what edition of BS7671 are you referencing?

The problem for electricians is that, while many domestic installations may not benefit much from the addition of surge protection, its omission is no longer a matter that can be settled by a customer simply declining the option and now requires a risk assessment. A comprehensive risk assessment takes a significant amount of time, for which the designer will receive no compensation, whereas inclusion of surge protection adds minimal cost to an installation. If you were designing installations, would you take the time to write up a risk assessment for every individual, in many cases finding yourself unable to remove the requirement of surge protection, or would you include it as part of the specification and save yourself considerable hours of unpaid work?
Such a risk assessment is super easy and super quick.
 
Such a risk assessment is super easy and super quick.

I can provide a risk assessment for anything within minutes, but producing one tailored to a particular installation that meets regulatory requirements and would stand up to legal scrutiny is another proposition entirely.

You didn't mention which edition of BS7671 you have referenced in previous comments.
 
  • Agree
Reactions: mainline
443.4.1 suggests options still exist, although limited.

It would be easy to take certain regulatory statements at face value and conclude that opinion of homeowner absolves designer of any responsibility, but 534.1 would also need to be considered and homeowner's thoughts on that are of no relevance.

GN1 also provides advice on this matter, but I don't have a current copy of it

I asked specifically what @slartybartfast was using as basis for their opinions as I suspect it is (now superseded) blue book.

I commissioned a board this evening in a newly rewired property and the homeowner expressed no opinion on fitment of SPD as I didn't ask for their thoughts on the matter. Difference in price between a main switch board and this main switch board with SPD (+ additional MCB) was £25+vat. If those few pounds had been a deal breaker, I suspect there were many other aspects of my quote that would have been more of a problem.
 
If, as should be done, a Hazard Analysis is carried out first and concludes that the Hazard does not exist or is of a very low consequence then a Risk Assessment does not have to be carried out.
 
I can see that there is an argument for SPD on say, mains powered linked smoke alarms (and medical, alarms etc). But you are far more likely to have a power failure which renders smoke alarm system inoperable than you are a surge. So for the SPD requirement to make sense, a UPS needs to be mandated. Mission critical systems always have a UPS and just putting an SPD on is a waste. That of course will come in later iterations of the regs....but for now it ain't there !
Placing a surge suppressor in front of the UPS isolates it and its connected equipment from major surge events. The IEEE Standard Section 9.11 states that networked SPD protection is needed and describes protecting a UPS with SPDs
 
If, as should be done, a Hazard Analysis is carried out first and concludes that the Hazard does not exist or is of a very low consequence then a Risk Assessment does not have to be carried out.
What's the difference between a Hazard analysis and a risk assessment when dealing with this scenario.
 
Last edited:
I can see that there is an argument for SPD on say, mains powered linked smoke alarms (and medical, alarms etc). But you are far more likely to have a power failure which renders smoke alarm system inoperable than you are a surge. So for the SPD requirement to make sense, a UPS needs to be mandated. Mission critical systems always have a UPS and just putting an SPD on is a waste. That of course will come in later iterations of the regs....but for now it ain't there !
There is no argument it's a requirement.

And even if the owner declares that surge protection isn't required, then the equipment still has to comply with the rated impulse voltage.
And would need to check that the data, signal, and telecom lines require protection to preserve lighting protection Zones LPZ concept 443.1.1, 534.1
 
Last edited:
What's the difference between a Hazard analysis and a risk assessment when dealing with this scenario.
They are two entirely different things in the scheme of Health and Safety, a Hazard analysis is always done first and then a risk assessment if necessary, it not always the case that the hazard has to be managed, the difference between the two are often miss-understood.
 
They are two entirely different things in the scheme of Health and Safety, a Hazard analysis is always done first and then a risk assessment if necessary, it not always the case that the hazard has to be managed, the difference between the two are often miss-understood.
An electrical hazard analysis identifies dangers that are present in an electrical system.

Mike Johnson said:
If, as should be done, a Hazard Analysis is carried out first and concludes that the Hazard does not exist or is of a very low consequence, then a Risk Assessment does not have to be carried out.


Are you saying that if there are no electrical hazards, then a risk assessment for fitting an SPD is not required ?
 
The first order of business in any H&S protocol is to eliminate the Hazard, If there is no hazards then a risk assessment is not required.
 
Last edited:
The first order of business in any H&S protocol is to eliminate the Hazard, If there is no hazards then a risk assessment is not required.

But you can't eliminate the chance of voltage surges, so a risk assessment is the thing to do.
 
There is no allowance for a risk assessment for the installation of SPDs anymore.

True, but I think most of this discussion has been around the previous guidelines/regs.
 
There is no allowance for a risk assessment for the installation of SPDs anymore.
The AQ criteria (conditions of external influence for lightning) for determining if protection against transient overvoltages is needed are no longer included in BS 7671. Instead, protection against transient overvoltages has to be provided where the consequence caused by overvoltage (see Regulation 443.4)

(a) results in serious injury to, or loss of, human life, or
(b) results in interruption of public services/or damage to and cultural heritage, or
(c) results in interruption of commercial or industrial activity, or
(d) affects a large number of co-located individuals.

For all other cases, a risk assessment has to be performed in order to determine if protection against transient overvoltage is required.
 
The AQ criteria (conditions of external influence for lightning) for determining if protection against transient overvoltages is needed are no longer included in BS 7671. Instead, protection against transient overvoltages has to be provided where the consequence caused by overvoltage (see Regulation 443.4)

(a) results in serious injury to, or loss of, human life, or
(b) results in interruption of public services/or damage to and cultural heritage, or
(c) results in interruption of commercial or industrial activity, or
(d) affects a large number of co-located individuals.

For all other cases, a risk assessment has to be performed in order to determine if protection against transient overvoltage is required.
You appear to be quoting the previous version of BS7671 here.

This is an extract from Amendment 2:

443.4 Overvoltage control

443.4.1 Transient overvoitages due to the effects of indirect lightning strokes


Protection against transient overvoltages shall be provided where the consequence
caused by the overvoltage could result in:

(i) serious injury to, or loss of, human life
(ii) failure of a safety service, as defined in Part 2
(iii) significant financial or data loss.

For all other cases, protection against transient overvoltages shall be provided unless the owner of the installation declares it is not required due to any loss or damage being tolerable and they accept the risk of damage to equipment and any consequential loss.
 
You appear to be quoting the previous version of BS7671 here.

This is an extract from Amendment 2:

443.4 Overvoltage control

443.4.1 Transient overvoitages due to the effects of indirect lightning strokes


Protection against transient overvoltages shall be provided where the consequence
caused by the overvoltage could result in:

(i) serious injury to, or loss of, human life
(ii) failure of a safety service, as defined in Part 2
(iii) significant financial or data loss.

For all other cases, protection against transient overvoltages shall be provided unless the owner of the installation declares it is not required due to any loss or damage being tolerable and they accept the risk of damage to equipment and any consequential loss.
Try chapter 44 Protection against voltage disturbances and electromagnetic disturbances.
 
True, but I think most of this discussion has been around the previous guidelines/regs.
I just skimmed the whole thread again, and you're correct, it dates back to before Amendment 2.
However, in the context of whether an SPD should have been fitted to an EV charge point, the previous version states that if a risk assessment is not carried out (and documented), then an SPD shall be fitted.

So the installer had no real reason not to fit one, unless they produced a documented risk assessment.
 
What do you think I just copied and pasted from? 🙄
Page 5

Chapter 44 Protection against voltage disturbances and electromagnetic disturbances

Section 443, which deals with protection against overvoltages of atmospheric origin or due to switching, has been redrafted.

The AQ criteria (conditions of external influence for lightning) for determining if protection against transient overvoltages is needed are no longer included in BS 7671. Instead, protection against transient overvoltages has to be provided where the consequence caused by overvoltage (see Regulation 443.4)

(a) results in serious injury to, or loss of, human life, or
(b) results in interruption of public services/or damage to and cultural heritage, or
(c) results in interruption of commercial or industrial activity, or
(d) affects a large number of co-located individuals.

For all other cases, a risk assessment has to be performed in order to determine if protection against transient overvoltage is required.

There is an exception not to provide protection for single dwelling units in certain situations.
 
Last edited:
Page 5

Chapter 44 Protection against voltage disturbances and electromagnetic disturbances

Section 443, which deals with protection against overvoltages of atmospheric origin or due to switching, has been redrafted.

The AQ criteria (conditions of external influence for lightning) for determining if protection against transient overvoltages is needed are no longer included in BS 7671. Instead, protection against transient overvoltages has to be provided where the consequence caused by overvoltage (see Regulation 443.4)

(a) results in serious injury to, or loss of, human life, or
(b) results in interruption of public services/or damage to and cultural heritage, or
(c) results in interruption of commercial or industrial activity, or
(d) affects a large number of co-located individuals.

For all other cases, a risk assessment has to be performed in order to determine if protection against transient overvoltage is required.

There is an exception not to provide protection for single dwelling units in certain situations.
Ah, I see where you're coming from.
I believe that section of page 5 is actually an error and should have been removed or reworded, as it is exactly the same as it is in the blue book. It contradicts what is actually said in section 443. It's only an introduction to BS7671:2018, and you'll notice the whole introduction is exactly the same as it is in the blue book, and makes no reference to the changes brought in with Amendment 2.

Also the On Site Guide pages 43 and 44 are in error.
 
But you can't eliminate the chance of voltage surges, so a risk assessment is the thing to do.
If the hazard analysis identifies a voltage surge as being possible? (with the main input isolated?) Then the next stage is the risk assessment.
 
If the hazard analysis identifies a voltage surge as being possible? (with the main input isolated?) Then the next stage is the risk assessment.
You seem to have a thing about this Mike!
I'm afraid I have to disagree with your treating the hazard analysis as a precursor to a risk assessment.
According to the steps outlined in many guides to risk assessment, the hazard analysis is the first step of the risk assessment process and it's therefore a part of the risk assessment, not a separate process.
May be just semantics, as the end result is the same.
An example downloaded from HSE:
 

Attachments

  • Like
Reactions: mainline and DPG
The reason the hazard analysis is a precursor to the risk assessment is if the analysis is able to eliminate the hazard the risk assessment is not needed.
 
As this has been dragged back up I will give an update..

Pod point eventually agreed to fit an SPD, I provided a 40A mcb in consumer unit, to a small 4way consumer unit with a double pole 32A RCBO with an SPD next to it, during install I was present and had to point out that the electrician had wired the SPD the wrong way round, I needed to then provide him with 6mm WAGO connectors as he cut the cables to short..

All good, but then no certificate, I chased and was sent the EIC, when I asked for the building regs certificate they said they would resend it, nothing came so I chased again and was told nothing to do with them and I needed to go to my local authority... I contacted NICEIC who were really good and checked, they had raised two building regs certificates so they deleted one and sent me a copy of the other...

Several months on I contact WPD to ask if they have sent paperwork for unlooping, nothing sent, I chase and ask them to send, after months of checking with WPD last month I finally got annoyed escalated it to pod point and they admitted they had not sent it as some MPAN number was wrong, I guess they were just going to do nothing with this even though they had a duty to inform WPD of the looped supply... Eventually that was sorted and I got a call from WPD within a week and they are going to extend the cable in the street and dig up my garden to run a new 3 phase supply to just outside the front door where they hope to intercept the loop cable, splicing the new cable on to that and terminating the other end coming from the neighbour so they dont need to be disturbed..

As for SPD's, well I went to many seminars and got told from the horses mouth by the guy involved in writing the regs from the IET, if you install a new circuit you must fit an SPD unless customer refuses, they cannot refuse on certain circuits... Move on to my NAPIT assessment and I get told an SPD is only needed if you change a consumer unit, if you are adding a new circuit to an existing consumer unit then its not needed, this was completely contradictory to what NAPIT confirmed with me when dealing with the EV charger..

So it seems like the powers that be can't decide, from a personal note with everyone doing their own electrics or getting dodgy electricians coming in I am putting electrical work on the back burner and going back into IT as a contractor for a bit as the work has dried up well unless you want to sign off some DIY'rs bodge job, I want to do a decent job but nobody wants to pay for it or appreciate it, I think ill still keep my insurance but will be dropping NAPIT as the cost just keeps going up and I don't get enough work that requires certification to warrant keeping it especially as ill mainly be doing IT contracting.. I guess the cost of living is hitting everyone so house building has stopped, nobody is getting extensions etc..
 
True, but I think most of this discussion has been around the previous guidelines/regs.

That's what I'd been trying to ascertain as the thread has been resurrected long since introduction of AM2, with statements being made that no longer apply.

I believe it's important that this distinction is made clear as, from other threads, it sould seem as though the member who resurrected the thread is (at the very least) keen to advise the electrician rewiring their property. It would be remiss of us to allow someone to labour under the misapprehension that a previous version of BS7671 is still relevant on this subject and to press their electrician toward a non-compliant installation.
 
  • Like
Reactions: DPG and loz2754
Try chapter 44 Protection against voltage disturbances and electromagnetic disturbances.

@loz2754 just quoted 443.4.1 from Chapter 44.

Oddly enough 3.7.2.1 of the new OSG quotes the very same regulation verbatim and then goes on to expand upon it with further advice that I can not find within the BB(rown)B.

Advice from OSG appears to deviate slightly from BBB, but the distinction is quite significant.
 
  • Like
Reactions: loz2754
The reason the hazard analysis is a precursor to the risk assessment is if the analysis is able to eliminate the hazard the risk assessment is not needed.

In the case of transient voltages due to the effects of indirect lightning strikes, how would one go about arguing that no hazard exists or eliminating the hazard entirely, without installing surge protection?
 
I suppose like all proof reading of publications, errors don't always get picked up. Seem to recall, has happened previously with BS7671.
 
I suppose like all proof reading of publications, errors don't always get picked up. Seem to recall, has happened previously with BS7671.

The additional information is lengthier than the regulation quoted before it. Worth looking at if you have both books to hand.

I'd quote it, but it's a lot to type.
 
@loz2754 just quoted 443.4.1 from Chapter 44.

Oddly enough 3.7.2.1 of the new OSG quotes the very same regulation verbatim and then goes on to expand upon it with further advice that I can not find within the BB(rown)B.

Advice from OSG appears to deviate slightly from BBB, but the distinction is quite significant.
It's an error, which I pointed out to the NICEIC instructor on my Amendment 2 course. He wasn't aware of it, but agreed that the OSG had retained a whole section that should have been deleted.
 
  • Like
Reactions: nicebutdim
  • Like
Reactions: nicebutdim
The reason the hazard analysis is a precursor to the risk assessment is if the analysis is able to eliminate the hazard the risk assessment is not needed.

In the case of transient voltages due to the effects of indirect lightning strikes, how would one go about arguing that no hazard exists or eliminating the hazard entirely, without installing surge protection?
Don't think of your individual situation think more global, think hazard first, identify and eliminate if possible, if not then complete a risk assessment.
 
  • Like
Reactions: nicebutdim
I was just trying to clarify for those that don't know that a Hazard Analysis is separate from the Risk Assessment and is carried out first with the main aim to eliminate the Hazard.
 
  • Like
Reactions: nicebutdim
Screenshot 2023-03-27 194323.jpg
 
  • Like
Reactions: nicebutdim
Process:
Step 1. Stop dicking about
Step 2. Spend £25 extra for an SPD
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
south west
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Are all EV charge point installers this bad?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
84

Advert

Thread statistics

Created
catdog1121,
Last reply from
Mike Johnson,
Replies
84
Views
13,501

Advert