Got a 7.5kw pump that’s blocked. Overload set to full load current of 13amp and fuses are BS88-2 20M25 but it keeps blowing the main fuses every time it’s blocked why would this be. The motor electrical is fine tested insulation resistance and resistance of winding. Thanks for your help in advance.
 
faulty overload, overload not removing power from main contactor, fuses are blowing before overload has heated up enough to trip contactor.
it is likely one of the above.
 
It is not really my area of expertise, but to me a 20M25 fuse is quite low for selectivity with a 7.5kW motor overload trip.

Usually the BS88 fuses are there for fault protection (i.e. to limit short-circuit I2t energy) and would be significantly larger than the overload trip than the factor of just under 2.5 here.

Hopefully someone else can comment?
 
Got a 7.5kw pump that’s blocked. Overload set to full load current of 13amp and fuses are BS88-2 20M25 but it keeps blowing the main fuses every time it’s blocked why would this be. The motor electrical is fine tested insulation resistance and resistance of winding. Thanks for your help in advance.
Locked Rotor when pump is jammed causing overcurrent hence fuse rupturing.
 

Reply to Thermal overload in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi I got called out to a faulty star delta starter on an old Stenner band saw Monday (was getting stuck in star and blow fuses) - So I ordered a...
Replies
19
Views
5K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock