How many different grades/capacities? Are there for 3x100amp coming in to the property?

I've seen 45kVA (seems low) and 70 kVA mentioned...are there others?

Also balancing the load...will they bill 3x the highest used phase?
 
Last edited by a moderator:
Your other 2 phases aren't currently in use.
They may have used up any spare capacity on those 2 phases somewhere else in the distribution network.

When you say not in use do you mean no load on them. Or might they not even be connected?
 
As a dno employee, it sounds as if you just need a straight forward meter change. You're load is well within the 100 amp supply. Just put the estimated load per phase. Don't worry about changing the existing customers, only needed if you have a high load on one phase creating problems. So 50 amps P1, 20 p2 , 10 p3 is not a problem. Half hour metering only applies to large power, where the MD ( maximum demand) is measured every half hour, if it goes over the agreed MD you pay extra.
 
Looks like I'll have to get someone else in to be safe....

I asked an electrician, he said the only thing that matters is the max demand figure. Told him what it was for...he just said to put 60-70 kVA.

As I say I don't even know what they're looking for in the 'maximum load reading for each phase'...is this also an estimate or an actual reading with a clamp meter or similar?
It’s basically a load sheet from the power company
 