Hi guys and girls,

I've been sent to an old house today to do an EICR on the property. All the circuits tested out fine both dead and live but when it came to getting a Zs reading for the main cables I couldn't get a reading at all. Upon further investigation I found the cables going from the time clock into the CCU are 230v between L and N but I'm not getting anything between L and Earth.

As said, on all 5 circuits I have full acceptable results.

This may be a silly question but as it's a TNC-S system does this mean I effectively have 2 neutrals and a live at every circuit?

If not is this acceptable? The RCCB still functions correctly so I'm assuming it IS an Earth.

If so does the test pass or do I have to get the DNO involved for a PME??

Sorry if this is a really silly query but it's been a while since I've done periodic testing as I'm so used to new build properties where you don't really need to think of these kind of things as it's so simple.
 
Last edited by a moderator:
If it TN-C-S you should be able to see the earthing conductor from the cut-out to the MET or direct into te consumer unit? You need to test Ze.
 
If it TN-C-S you should be able to see the earthing conductor from the cut-out to the MET or direct into te consumer unit? You need to test Ze.

As he said you should see the earth conductor clearly going to the MET to take your reading.
 
Do a PSC connected to the earth and then the same test to Neautral, if its a TNCS the readings will be the same.
 
It comes out at 0.33 between L and N and it won't even test between L and Earth. Its a Fluke 1652.
 
a photo of the cut-out and surrounding area including the MET and the CU with cover off would help.
 
are you sure its tncs just because its connected as tncs dont mean it is best bet is to enquire to dno about earthing system
 
meanwhile , start bashing in a screwed together rod system.
 
So you do not have pme because you do not have a Ze. The final circuits may be testing out ok but they will be getting an earth from elsewhere, probably the water or gas incoming service pipe. Is there a label on the cut-saying it is a pme system? Either way ring the DNO.
 
Live and neutral 230, with nothing between live and earth? Have you tried testing between neutral and earth? If you get 230 then you've got live neutral reverse
 
Definitely check that, but the OP did say everything tested out ok on the final circuits. Including presumably live polarity testing. Unless its double crossed!
 
needs a pic to comment further.
 
Yeah cheers guys.

As the property is vacant I have left the board off and advised the DNO to be informed. L-N reverse was eliminated very early but it was considered.

Bloomin' frustrating this sparkying lark sometimes isn't it??
 
Just a thoughht here but a Ze and a Zs test (on my gear anyway) requires 3 leads. If I have the leads the wrong way round my tester tells me. Surely if this was a straight polarity issue then something should have happened to alert you to it.
 