Thanks for all your help. I told my office the situation and they got in touch with, I assume, the DNO and apparently it used to be a TN-C system but they had an earth fault so a temporary TT system was put in. This temporary system has now been there for 20 years!!

It explains why there was an earth at every circuit but not at the MET. And as a side, there was me there yesterday and 2 guys there this morning and no one can find where they've spiked into the earth!
 
After 20 years it might be a struggle to get them to maintain their earth so you might have to do some work on that TT mate.
 
After 20 years it might be a struggle to get them to maintain their earth so you might have to do some work on that TT mate.


Well if I were a one man band I'd do so but as I work for a company who's only goal is to make money I've been instructed to leave it off until they get paid for doing the works.

Surely it requires a new mains which would be down to Southern Electric or whomever? A TT system in a suburban neighbourhood seems mental.
 
Nothing wrong with a TT in an urban environment mate, my house is on a busy road not far from the town centre and is a TT. when I rewired it I did a good bit of work to make sure I got it down to TN level. It's not that hard if you put your mind to it.
The rule is that if they provide an earth they have to maintain it so it's their problem normally, whether they could be pushed enough to sort it after 20 years is another matter entirely though.
 
Yeah I guess so pal. I've not been back in the domestic game for a good while and live in London so TT systems are few and far between! Still, was fun figuring it out. I had a feeling in the back of my mind that they'd brought a new earth from somewhere but no one can find the bloomin' earth spike!!
 
It's under the paving with Fred West's last victims and that bloke the dyke killed on that soap opera years ago. Find another position, drive two rods coupled together and hook it back up. You'll get a lot lower result
 
Definitely check that, but the OP did say everything tested out ok on the final circuits. Including presumably live polarity testing. Unless its double crossed!
do you actually know anything at all?.....*abrasive, removed*

to the O/P....the circuits you dead tested will have shown good continuity of R2....
that doesn`t mean a good Zs is guarenteed...does it....
you think about it....
 
Last edited by a moderator:
This was you reply to my post (no. 2). I'm not sure what you thought was incorrect, perhaps you could enlighten me?
what ?...is that all you have
...first year visual stuff....
*abrasive, removed*
 
Last edited by a moderator: