Andy-1960

-
Esteemed
Arms
Reaction score
575
What are the thoughts of you guys on the differences between a TN-S and a TNC-S (PNB) Earthing System.

My understanding is as follows:

TNC-S (PNB) - the Neutral & Earth Conductor are joined in the main switchboard with the neutral conductor between the transformer and the switchboard then being the earth fault path back to the transformer star point.

TN-S -a separate earth conductor is installed between the transformer and the switchboard and the neutral and earth are joined in the transformer cable box, the earth fault path back to the transformer start point.

So, depending on your thoughts, would you then say the source of supply is the switchboard or the transformer... I know what I think, but I have a customer who disagrees.
 
the source of the supply is the customer's DNO fuse/s.
 
This has been chewed over many a time. Some argue the neutral from the transformer star point to the customers panel does not have a combined function, it is merely moving the star point to the panel where the earth is taken from so at this point it is TN-S. Others argue the reverse that the neutral does have a combined PEN function and is not shifting the star point from the transformer hence PNB.
 
PNB is TNS. It cannot be TNC-S as there is no conductor that shares the "earth" and "neutral" functions. It also cannot be "PME" as there is only a single connection to earth. PNB is used where a transformer supplies a single large customer. The earth reference for the transformer star-point is made at the customer's end of the supply cable, as there will not usually be a fuse rack in the DNO's substation.
 
In the UK, it’s very rare to find a link between neutral and earth within the customer’s installation.
PNB as Buzz says is more akin to TN-S as it uses separate conductors. However it is treated in the UK as being TN-C-S.

It’s not correct to say there is only one connection to earth.
It will depend on the distance between the transformer and the installation.
Could be just the one electrode and link somewhere between, or there could be two, one close to the transformer and the other close to the installation.
 
PNB is TNS. It cannot be TNC-S as there is no conductor that shares the "earth" and "neutral" functions. It also cannot be "PME" as there is only a single connection to earth. PNB is used where a transformer supplies a single large customer. The earth reference for the transformer star-point is made at the customer's end of the supply cable, as there will not usually be a fuse rack in the DNO's substation.
christ buzz, you been eating dictionaries?
 
christ buzz, you been eating dictionaries
url-3-10tjli1.jpeg
yep.
 
A TN-S will have a single earth conductor from the star point of the DNO transformer.

As in ‘S’ - seperate

A TN-C-S is combined on the DNO side ‘C’ and seperate on the installation side ‘S’.

A PME will be earthed at multiple points along the PEN conductor and then linked out at the termination within the installation.

A PNB will only be linked out at the installation with no other earthing points. As soon as another earthing point is put in along the PEN conductor it ceases to be a PNB.
 
A TN-S will have a single earth conductor from the star point of the DNO transformer.

As in ‘S’ - seperate

A TN-C-S is combined on the DNO side ‘C’ and seperate on the installation side ‘S’.

A PME will be earthed at multiple points along the PEN conductor and then linked out at the termination within the installation.

A PNB will only be linked out at the installation with no other earthing points. As soon as another earthing point is put in along the PEN conductor it ceases to be a PNB.
If it has a PEN conductor, then it’s TN-C-S.
 
PNB is TNS. It cannot be TNC-S as there is no conductor that shares the "earth" and "neutral" functions. It also cannot be "PME" as there is only a single connection to earth. PNB is used where a transformer supplies a single large customer. The earth reference for the transformer star-point is made at the customer's end of the supply cable, as there will not usually be a fuse rack in the DNO's substation.
735-6.jpg
 

Reply to TN-S vs TNC-S (PNB) Earthing System in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
676
Hi all, For clarity, I'm not a qualified electrician, but have a reasonable amount of experience as I've done plenty of wiring (signed off by a...
Replies
19
Views
3K
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock